Question

How does flow rate affect the individual heat-transfer coefficients on the tube and annular sides of the exchanger? Explain i
0 0
Add a comment Improve this question Transcribed image text
Answer #1

The local heat transfer coefficient increases as the mass flow rate increases. The heat flow from the pipe wall in a length dx is

\dot{q}\pi Ddx=h\pi D(T_{0}-T)dx

After the integration from limits T1 (temperature at inlet x=0) to T in a length 0 to x

To-T 4h.r Pum CpD

The temperature at the exit of the heat exchanger is T= T2 at x=L

4hL rl

The overall heat transfer coefficient is constant throughout the heat exchanger as per the LMTD assumption.

1/ hyi

Add a comment
Know the answer?
Add Answer to:
How does flow rate affect the individual heat-transfer coefficients on the tube and annular sides...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • at Your objective in this problem is to design a "simple" annular flow heat exchanger (see...

    at Your objective in this problem is to design a "simple" annular flow heat exchanger (see the "simple" description the beginning of this HW). A heat exchanger of this kind can easily be built in your garage with two different size pper pipes along with some solder. Assume both fluids are water with the cold fluid flowing in the outer tube. The pipe diameters are based in Type L copper tube dimensions: outside diameter 1/2 -inch nominal tube is 0.625...

  • Hot water flows thorough a parallel flow heat exchanger at a rate of 10 kg/min and...

    Hot water flows thorough a parallel flow heat exchanger at a rate of 10 kg/min and is cooled by a cold water stream of flow rate 25 kg/min. The inlet temperatures of hot and cold water streams are 70 oC and 25 oC, respectively. The outlet temperature of the hot water is expected to be 50 oC. The individual convective heat transfer coefficient on both sides of the heat transfer area is 600 W/m2 .K. Take the specific heat for...

  • Question 5 The following data is given for counter flow in concentric tube heat exchanger, mean...

    Question 5 The following data is given for counter flow in concentric tube heat exchanger, mean heat transfer area = 0.02 m2 Test No Flow rate hot Flow rate Tin hotTout hot|Tin cold Tout cold (L/min) cold (L/min) (THI) (TH2) (TCI) (TC2) 13 1 60 56 30 42 a) Calculate the heat transfer rate in kW. b) The overall heat transfer coefficient U. c) The mean temperature efficiency of the two circuits (ń).

  • A counter-flow heat exchanger is stated to have an overall heat transfer coefficient of 284 W/m2.K...

    A counter-flow heat exchanger is stated to have an overall heat transfer coefficient of 284 W/m2.K when operating at design and clean conditions. Hot fluid enters the tube side at 101°C and exits at 71°C, while cold fluid enters the shell side at 27°C and exits at 42°C. After a period of use, built-up scale in the heat exchanger gives a fouling factor of 0.0004 m2 K/W. The surface area is 93 m². Assume both hot and cold fluids have...

  • please do 11.33 11.32 A single-pass, cross-flow heat exchanger uses hot exhaust gases (mixed) to heat...

    please do 11.33 11.32 A single-pass, cross-flow heat exchanger uses hot exhaust gases (mixed) to heat water (unmixed) from 30 to 80°C at a rate of 3 kg/s. The exhaust gases, hav- ing thermophysical properties similar to air, enter and exit the exchanger at 225 and 100°C, respectively. If the overall heat transfer coefficient is 200 W/m2.K, estimate the required surface area. 11.33 Consider the fluid conditions and overall heat transfer coefficient of Problem 11.32 for a concentric tube heat...

  • Oil of unknown properties is heated in a shell-and-tube heat exchanger with one shell pass and...

    Oil of unknown properties is heated in a shell-and-tube heat exchanger with one shell pass and 20 tube passes. The oil flows through the shell, and hot water flows inside the single copper tube that has an inner diameter of 20 mm, a wall thickness of 2 mm, and a length of 3 m per pass. The water enters at 360 K at a mass flow rate of 0.2 kg/s and leaves at 300 K. The inlet and outlet temperatures...

  • A simple counter flow heat exchanger consists of two co-axial tubes with hot process water passing...

    A simple counter flow heat exchanger consists of two co-axial tubes with hot process water passing through the inner tube and clean water through the annular space between the inner and outer tubes. The clean water enters at 20°C and leaves at 50°C. The process water enters at 90°C and leaves at 40°C. The mass flowrate of the process water is 3 kgs-1. The inner tube diameter is 30 mm and the outer tube diameter is 50 mm. Take the...

  • Twenty [kw] of heat is to be removed from 375 [k] water flowing at 0.15 [kg/s] into the inner pipe of concentric tube heat exchanger. Cooling water enters the annulus at 290 [k] and leaves at 320...

    Twenty [kw] of heat is to be removed from 375 [k] water flowing at 0.15 [kg/s] into the inner pipe of concentric tube heat exchanger. Cooling water enters the annulus at 290 [k] and leaves at 320 [k] with a flow in the opposite direction of the inner flow. The diameter of the thin- walled inner pipe is 2.5 [cm] a) b) c) Calculate the exit temperature of the hot fluid and the mass flow rate of the cold fluid...

  • heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes,...

    heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes, each executing two passes, is used in a large steam power plant to condense steam to liquid water. The steam condensed in the shell side of the heat exchanger with an associated convection coefficient (h) of 11.000 W/m2.°C. The heat transfer rate through the heat exchanger (O is 2x10' W. Cooling water is passing through a thin tubes with D = 2.5 cm, at...

  • Heat transfer 1) 2.5 m/s of air at 150°C is used to heat (0.25 + /250)=0.254...

    Heat transfer 1) 2.5 m/s of air at 150°C is used to heat (0.25 + /250)=0.254 kg/s of 20°C water. The heat exchanger is a finned-tube cross flow heat exchanger with both sides unmixed. The overall heat transfer coefficient associated with the hot side is 120 W/(m2 °C). The hot-side area is 20 m². Assume a constant specific heat for air and water of Cecair = 1.005 kJ/(kg °C), Crewater = 4.2 kJ/(kg). The pressure of the hot air is...