a. the sensible heat ratio (SHR) for the cooling and dehumidifying process; (2 Marks) b. the supply air volume flow rate to the office in m3 /s; (5 Marks) c. the air dry bulb temperature and specific enthalpy of the mixture of outdoor and recirculating air; (4 Marks) d. the cooling coil’s load in kW. (5 Marks) e. the apparatus dew point during the cooling and dehumidifying process; and (4 Marks) f. Discuss, with reasons, the possible effects on the CAV system if people are bringing in a large number of hot lunch boxes into the office due to the policy of Novel Coronavirus. (5 Marks)
a. the sensible heat ratio (SHR) for the cooling and dehumidifying process; (2 Marks) b. the...
Subject Refrigeration and Air Conditioning. Please answer in detail. QUESTION 4 - COOLING AND DEHUMIDIFYING COILS An air conditioned space at 1700 metres altitude has a sensible heat gain of 26 kW and a latent heat gain of 6.5 kW. The space is maintained at 25°C dry bulb and 18°C wet bulb temperature:s The fresh air supply is to be 0.65 m3/s at 35°C dry bulb and 24°C wet bulb temperatures. The air leaving the coil has a relative humidity...
Question NO. 3 (25 points) A space to be maintained at 27°C dry-bulb temperature has a rate of sensible-heat gain of 13 kW and a rate of latent heat gain of 8.5 kW. The system used to condition the space to the required conditions. The mass flow rate of air supplied to the space is 1.1 kg/s. Outdoor air at 38 °C dry-bulb temperature and 17 ℃ dew-point temperature is introduced into the system at a rate of 0.28 kg/s....
A building is designed for the following cooling loads. Room specific heat gain and latent heat gains are 310 kW and 100 kW respectively. The room is maintained at a dry bulb temperature of 25°C and relative humidity of 50%. The outdoor air is at 28°C with 50% relative humidity, 10% by mass of outdoor air is supplied to the building. If the air supplied to the room should be at a temperature lower than 18°C, detemine the following. (a)...
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...
a) What is the difference between latent and sensible heat gains in building cooling load analysis? Provide examples of each (2 marks) b) In heating load calculations, it is a normal practice to neglect the solar heat gain Explain why. (2 marks) c) An air conditioned single family detached house with a Figure_Q6A is located in Perth, Australia (Latitude 31° South). The ceiling height is 24 m. The summer floor plan shown in design indoor temperature is 25°C. Outside design...
A summer air conditioning system with recirculating air stream and BPF = 0 has a room sensible heat load of 20 kW and a room latent heat load of 2.22 kW. The required inside conditions are 22°C and 50% RH, and the outdoor design conditions are 36°C and 60% RH. The mass flow rate of the outside air is 15% of the mass flow rate of the supply air. Find a) RSHF b) the point s on the chart, mass...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...
Prob. # 2] The temperature to be maintained in an office building is 26 C DB heat is 77.6 kW and the latent heat gain is 14.3 kW. Th accomplished by passing it through a spray-type heated to 18 C then supplied to the room. Find and 18 C W B. The sensible e cooling and dehumidifying of the air is washer with water chilled by refrigeration. The air is then a. the apparatus dew point temperature of washer, b....
o question: An airconditioned space is to be maintained at 26 C dry bulb temperature and 50% RH. The ambient condition is 4 27.78 kW and the latent load is 11.11 kW. 60% of the return air mass is recirculated and mixed with 40% of make-up fresh air before entering the AHU. Calculate: Room SHF -Supply flow rate (m'/sec) (assume supply temperature is 10 C lower than space's) Apparatus sensible and latent load Apparatus sensible heat factor, dew point, and...