(10%) Problem 7: Suppose a large power plant generates electricity at 12.0 kV. Its old transformer once converted this voltag

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Part(a):-Output power with old transformer-

  P = 1000MW = 1000 x 106W = 10w

Output voltage-

Vout = 345KV = 345 x 103V = 3.45 x 10 V

Output power-

P= Vout lout

P — Iout = Volt

109 Lout = 3.45 x 105

lout = 2.899 x 103 A

Power loss in lines-

Ploss = IR

Ploss = (2.899 x 1032 x 2

Ploss = 1.68 x 10W

------------------------------------------

Part(b)-In this case-

Tout = Vout

\mathbf{I_{out}=\frac{10^9}{760\times 10^3}}

\mathbf{I_{out}=1.316\times 10^3W}

power loss in lines-

\mathbf{P=I_{out}^2R}

\mathbf{P=(1.316\times 10^3)^2\times 2}

Ploss 2 = 3.46 x 100W = 3.46MW

Add a comment
Know the answer?
Add Answer to:
(10%) Problem 7: Suppose a large power plant generates electricity at 12.0 kV. Its old transformer...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Suppose a large power plant generates electricity at 12.0 kV. Its old transformer once converted this voltage to kV. The secondary coil of this transformer is being replaced so that its output can be...

    Suppose a large power plant generates electricity at 12.0 kV. Its old transformer once converted this voltage to kV. The secondary coil of this transformer is being replaced so that its output can be 730 kV for more efficient cross-country transmission on upgraded transmission lines V 315 kV V2 730 kV - 50% Part (a) If the overall power output is 1000.0 MW and line resistance is 2.00 Ω, what was the power loss, in watts, in the old power...

  • A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage...

    A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 345 kV. The secondary of this transformer is being replaced so that its output can be 775 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 2.950, what are the old and new line power losses (in MW)? old line losses X MW new line losses 198 X MW

  • A large power plant generates electricity at 12.0 KV. Its old transformer once converted the voltage...

    A large power plant generates electricity at 12.0 KV. Its old transformer once converted the voltage to 340 KV. The secondary of this transformer is being replaced so that its output can be 775 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 2.050, what are the old and new line power losses (in MW)? old line losses 1.7734 MW new line losses 3.413 MW 7

  • A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage...

    A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 350 KV. The secondary of this transformer is being replaced so that its output can be 765 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 2.750, what are the old and new line power losses (in MW)? old line losses new line losses MW MW

  • A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage...

    A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 325 kV. The secondary of this transformer is being replaced so that its output can be 775 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 2.150, what are the old and new line power losses (in MW)? old line losses MW new line losses MW 1 Submit Answer

  • A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage...

    A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 330 kV. The secondary of this transformer is being replaced so that its output can be 775 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 1.20 Ω, what are the old and new line power losses (in MW)? old line losses. new line losses physics

  • 5.35/b.bb Poi PREVIOUS AN OSCOLPHYS2016 23.7.P.051. ME A large power plant generates electricity at 12.0 kV....

    5.35/b.bb Poi PREVIOUS AN OSCOLPHYS2016 23.7.P.051. ME A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 340 kV. The secondary of this transformer is being replaced so that its output can be 775 kV for more efficient cross-country transmission on upgraded transmission lines. If the power output is 1,000 MW and line resistance is 2.050, what are th old and new line power losses (in MW)? old line losses X MW Enter...

  • What is the peak emf generated (in V) by rotating a 1000 turn, 10.0 cm diameter...

    What is the peak emf generated (in V) by rotating a 1000 turn, 10.0 cm diameter coil in the Earth's 5.00 ✕ 10−5 T magnetic field, given the plane of the coil is originally perpendicular to the Earth's field and is rotated to be parallel to the field in 17.0 ms? =______V A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 325 kV. The secondary of this transformer is being replaced so...

  • a power plant has 4 smaller substations. the main power plant generates 420 MW of electricity...

    a power plant has 4 smaller substations. the main power plant generates 420 MW of electricity and is distributed to these substations using high voltage power lines. Each line carries 140 kV while having .20 Ohms resistance in each line. what is the power loss in each transmission line? let the power be distributed equally betewen the 4 substations. 12000 kW 2000 kW 900 kW 4000 kW 450 kW 110 kW

  • I really need some help with part a part B and part see if you could...

    I really need some help with part a part B and part see if you could please explain how you got the answer that would be great! Class Management | Help Online HW#7 Begin Date: 2/17/2020 12:01:00 AM - Due Date: 3/9/2020 11:59:00 PM End Date: 5/9/2020 11:59:00 PM (11%) Problem 5: A large power plant generates electricity at 12.0 kV. Its old transformer once converted the voltage to 355 kV. The secondary coil of this transformer is being replaced...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT