Question

Page 2 of 8 May 2018 16-MEC-B2 Environmental Control in Buildings ROBLEM 1. (30 POIN In sumimer a room is to be maintained at

Please provide detailed solution with schematic diagram and psychometric chart. your highly response will be appreciated.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Please take a note that the outlet of heating coil is less than 2 centigrade of the supply condition.

Feel free to ask any doubts regarding this question .

Thanks

Enjoy refrigeration and air-conditioning!fig schemonc cianam Ma 20 L 9-50% |Room o) 26 Fotshour Miyi Coil Coi Cham Frshair+ 2 dehunidititaion ADR ouside aiy i 0.0073d.a 0.1 72-7A =11 x 26) + (2x 20 Dp T- TADP 42-i el _ 16-assilas w,2-wapp 咬-o.oo5 1 - as-y 2 19 29 66 ka sa d Cooing Coit loa

Add a comment
Know the answer?
Add Answer to:
Please provide detailed solution with schematic diagram and psychometric chart. your highly response will be appreciated....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • O question: An airconditioned space is to be maintained at 26 C dry bulb temperature and 50% RH. ...

    o question: An airconditioned space is to be maintained at 26 C dry bulb temperature and 50% RH. The ambient condition is 4 27.78 kW and the latent load is 11.11 kW. 60% of the return air mass is recirculated and mixed with 40% of make-up fresh air before entering the AHU. Calculate: Room SHF -Supply flow rate (m'/sec) (assume supply temperature is 10 C lower than space's) Apparatus sensible and latent load Apparatus sensible heat factor, dew point, and...

  • PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (we...

    PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (wet bulb) has a rate of sensible-heat gain of 25 kWand a rate of moisture gain of20 kg/hr. Moist air enters the space at a dry-bulb temperature of 15°C. Outdoor air at 35 C dB temperature and 25 C wB is supplied for ventilation purposes at a rate of 400 Us (litres per second) of standard air. After leaving the room,...

  • An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the...

    An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...

  • Question 4 Page 15 It is required to 125 marks] design a cold storage for storing...

    Question 4 Page 15 It is required to 125 marks] design a cold storage for storing vegetables with the following available data Outside design conditions 36°C DBT. 28 C WBT Inside design conditions T2 19°C DBT, 60% RH Infiltrated air 180 mhr V ms-7.83 kg/s Fresh air supplied from outside 4500 mhr Total mass of air supplied to the room Sensible heat gain through glass SH,5.5AW Sensible heat gain through walls and roof H 10.8 kW Ihr KJ Sensible heat...

  • 4. Air-Conditioning Unit [20 Marks] 1 m3/s of moist air at 32 °C with a relative...

    4. Air-Conditioning Unit [20 Marks] 1 m3/s of moist air at 32 °C with a relative humidity of 70% is to be treated by a simple air condition system to produce air at 18 °C with a relative humidity of 50% The system will have two stages. In the first stage, the air will pass over cooling coils to dehumidify it, and in the second stage it will be heated electrically to the specified outlet conditions You may ignore the...

  • summarizr the followung info and write them in your own words and break them into different...

    summarizr the followung info and write them in your own words and break them into different key points.   6.5 Metering Chamber: 6.5.1 The minimum size of the metering box is governed by the metering area required to obtain a representative test area for the specimen (see 7.2) and for maintenance of reasonable test accuracy. For example, for specimens incorporating air spaces or stud spaces, the metering area shall span an integral number of spaces (see 5.5). The depth of...

  • summatize the following info and break them into differeng key points. write them in yojr own...

    summatize the following info and break them into differeng key points. write them in yojr own words   apartus 6.1 Introduction—The design of a successful hot box appa- ratus is influenced by many factors. Before beginning the design of an apparatus meeting this standard, the designer shall review the discussion on the limitations and accuracy, Section 13, discussions of the energy flows in a hot box, Annex A2, the metering box wall loss flow, Annex A3, and flanking loss, Annex...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT