If electricity costs $0.08/kWH, and a grocery store operates its lighting system for 8,760 hours annually, what is the estimated annual cost to operate the grocery store lighting system? The light fixtures used are two-lamp fluorescent troffers (each lamp used 40W) and there are 140 troffer fixtures in the store.
Select one:
a. $7,850 per year
b. $4,835 per year
c. $12,280 per year
d. $3,925 per year
e. $7,700 per year
Answer_a ) 7850 dollars per year
I have shown the calculation for the answer so that you can understand the solution easily. Hope you like the solution. Thank you.
If electricity costs $0.08/kWH, and a grocery store operates its lighting system for 8,760 hours annually,...
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...