Question

Question 8: Using a typical frequency response illustrate the different hierarchies of frequency control in large-scale power
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Hierarchies in Large Scale Power Systems:

Because of their complex structures and large sizes, electric power networks are typically monitored and controlled according to their hierarchical structures. Instead of modeling the intricate dynamics of the entire system, the system dynamics is modeled by deriving submodels relevant for each particular sub-process. This is based on observing different time scales over which sub-processes evolve under certain assumptions. The overall system behavior can be fully portrayed by piecing together those simpler, yet essential, elements. The theoretical basis for this type of modeling in large electric power systems was introduced in [8]. The basic submodels are the
(i) primary (local) model at a device level, (ii) secondary (area-wide) level for each administrative area, and (iii) tertiary (global) level representing the interconnected system, Figure 2-1.
The primary control level is entirely decentralized at present. Within this level, controllers respond to the small but fast local disturbances appearing at the terminals of each generator. The speed governor units in electric machines maintain the control of this level. Primary controllers stabilize system dynamics within a very short time constant, T,, i.e., on the second scale, with the performance specification of a minute,
or so.
The secondary control level is decentralized and is particularly useful in analyzingand controlling the dynamic performance within an administrative area (subsystem level). This model represents all generators and large number of loads connected by transmission lines in each administrative area. The secondary control is implemented at a slower time scale, T,, than that of the primary control (i.e., T, is typically on the several-second scale, with the performance objective over 10 minutes, or so). The secondary control is intended to stabilize system outputs within the administrative area that are disturbed by changes within the area as well as by the changes in neighboring areas. Presently implemented AGC is based on this control structure. Seen from the interconnected system level, each subsystem uses AGC using decentralized
measurements at its own level only. The theoretical tertiary control level is coordinated. The aggregate tertiary-level models describe the inter-area dynamics among administrative areas and are useful for regulating inter-area variables such as tie-line power flows. These models evolve
on an even slower time constant, Tt, than the secondary level rate, Ts, i.e., on the minute scale. This higher level structure is not currently used in the utility industry.
However, its importance is increasing as the electric power market is changing and becoming more competitive. It is plausible that in the future, decentralized regulation
at the secondary-level would not be sufficient to respond to intense interactions among the areas under an open access environment. The later parts of this thesis provide examples illustrating potential problems of this sort.
Hierarchical level models higher than the tertiary control level described in this topic can also be developed. For example, in present utility industry, the control centers reset the scheduled values of transmission power among the areas and the phase angle of the slack generator at a much slower rate for economic reasons. The unit commitment procedures such as turning on- and off- the available generators in anticipation of demand on a daily basis, is yet another process of interest. These processes, at least in concepts, could be regarded as evolving at hierarchies beyond the tertiary level. However, these models are beyond the scope of this topic.

Tertiary Secondary // a rimary く Area 4 Area Area 3 Area 2 G GeneratorDemandssutio? Given isolated snchronou genesator rated Capacity-115ma ะ Rated Thee lood mitiallu 3 xLtmw (fmo) added 3.Smul (t-?) (스イ. а.SH3ィ(-0.s) 2Ha This is the presnt Regitny t uwhich genrotes i opexatii uenu at

Add a comment
Know the answer?
Add Answer to:
Question 8: Using a typical frequency response illustrate the different hierarchies of frequency control in large-scale...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Question 8: Using a typical frequency response illustrate the different hierarchies of frequency ...

    Question 8: Using a typical frequency response illustrate the different hierarchies of frequency control in large-scale power system. Discuss and illustrate using a numerical example why governors using speed droop or speed regulation cannot alone restore the power system frequency to the pre-disturbance level. Question 9: An isolated 50 Hz synchronous generator is rated at 15 MW which is also the maximum continuous power limit of its prime mover. It is equipped with a speed governor with 5% droop. Initially,...

  • I need help to solve this questions about Generator Governor Droop and Transmission Line. A complete...

    I need help to solve this questions about Generator Governor Droop and Transmission Line. A complete solutions with answers would be great. Thank you Generation Question 1 to 5 relate to the following grid connected generator. A governor-controlled, steam-driven 450 MW synchronous generator with 5% droop is synchronized to the 60 Hz grid and its load set-point adjusted to deliver 300 MW to the grid. Q1. (a) 000 What is the actual droop of the generating unit? 0.0225 Hz/MW (b)...

  • Could you please help solve this question. The following generator supplying rated load into a large...

    Could you please help solve this question. The following generator supplying rated load into a large grid at rated voltage (11kV) and 0.85 PF lagging Generator: 20 MVA, X = j15%. Voltage 11kV i) Determine the internal generator voltage. ii) The load suddenly drops to 50% rated power. If the rotating energy of the generator and its associated turbine is 2.0 p.u-seconds when running at its synchronous speed. It has 2 poles and system frequency is 50 Hz. Determine: (ii-a)...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT