Question

The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied...

The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied to the secondary gave a wattmeter reading of 60 W and secondary current of 10 A. II the normal applied primary voltage is 200 V, the transformation ratio 1:2 and the full-load secondary current 10 A, calculate the secondary p.d. at full-load current for (a) unity power factor (b) power factor 0.8 lagging.

these are the answers [ 394 V; 377.6 V ]

1 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited...

    A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...

  • Three-phase, 50Hz, 6600/1000/440 Y V transformer

    A 3-phase, 50 Hz, 6600 /1000  /440 Y V. transformer. 1. Determine suitable numbers of turns to ensure the peak flux does not exceed 0.03 Web.                                                                                                            2. Determine the...

  • Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary...

    Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary Voltage Excitation reactance Series Impedance 150 MVA 230 kV 32 kV 30 (pu) 0.02+0.15j (pu) The transformer is Y/A connected. Answer the following questions: a) What are the nominal (rated) primary and secondary line currents?| b) What is the nominal value of the Delta-side winding (internal) current? c) What is the secondary to primary winding turn ratio? d) The transformer is supplying 150 MVA...

  • A 3-phase, 50 Hz, 6600 /1000 /440 Y V. transformer (HELP)

    Question: A 3-phase, 50 Hz, 6600 /1000  /440 Y V. transformer. (i) What is the purpose of using three winding transformers?                      (ii)Determine suitable numbers of turns to ensure the peak flux does not exceed 0.03 Web.                                                                                                            (ii) Determine the primary line current and power factor if the 1000 V winding delivers a balanced load of 100 kVA at 0.8 power factor lagging and the 440 V winding delivers a balanced load of 50 kW at unity power factor.                            

  • Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under...

    Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under short-term overload conditions at an 0.8 power factor leading and at 230 volts. Reference of problem 3.4 A single phase 100-kVA 2400/240-volt 60 Hz distribution transformer is used as a step down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 60kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary...

  • Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz...

    Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA at 0.8 p.f. lagging Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA...

  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

  • A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which...

    A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary voltage. b) load impedance. c) load impedance referred to the primary. d) the real and reactive power supplied to the primary winding

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • The following data was obtained when open circuit and short circuit tests were performed on a...

    The following data was obtained when open circuit and short circuit tests were performed on a single phase, 50 KVA, 2,400:240 V, 60 Hz distribution transformer: With high voltage winding open circuited: Voc = 240 V, Ioc = 4.85 A, Poc = 173 W With low voltage winding short circuited: Vsc = 52 V, Isc = 20.8 A, Psc = 650 W a) Determine the equivalent circuit of the transformer referred to its high voltage side and to its low...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT