Question

The portion of structure shown represents the upper part of a power transmission line tower. For the given loading, determine

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solution: foee body : Joint A: FAB FAC 2.29 FAB FAC 1:2 1-2 KN 2.21 J-2 2.23 1.2 2.23 L0.6 fAB FAc FAB = 2.29 kn CT)- 1:2KN.foee body:Joint c: Fsc = 0.600kN + Ef = o 2.21 2.21 -× 2.29 =O Jo.6 2.29 FAC 2.29 FeE =2.29 KN. FEE = -2. 2) KN. FcE (c) +- =

Add a comment
Know the answer?
Add Answer to:
The portion of structure shown represents the upper part of a power transmission line tower. For...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Fa A truss structure is used to build the transmission tower shown with dimensions and loads...

    Fa A truss structure is used to build the transmission tower shown with dimensions and loads shown below. Assuming the structure does not deform out-of-plane, and that none of the members buckle, find the force and stress that each member named in the table below carries and the change in length of each of those members if they are composed of structural steel 1.8 m 4.5 m 2.7 m 8.8 m 8.1 m 4.4 kN 68 deg 3.5 k Membens...

  • 700 kN C- Diagram for Question 3 6 m A tower used for a highline is...

    700 kN C- Diagram for Question 3 6 m A tower used for a highline is shown in the figure at the left. If it is subjected to a horizontal force of 700 kN and the allowable stresses are 80 MPa in compression and 180 MPa in tension, what is the required cross-sectional area of each member (there are 7 members)? All members are pin-connected. All dimensions are in metres. Note also that BC and AD are not connected where...

  • 1. For the structure shown, P1 = 20 kN and P2 = 30 kN. Find the...

    1. For the structure shown, P1 = 20 kN and P2 = 30 kN. Find the force in each member. State whether each member is in tension or compression ,N 1.5 m 2 m F60 = 20K Comp Bo = 33.33K TEISION I For= 56.66 Kal Comp

  • USE ANSYS (no hand calculations) Consider the power transmission-line tower shown in the accompanying figure. The...

    USE ANSYS (no hand calculations) Consider the power transmission-line tower shown in the accompanying figure. The members have a cross-sectional area of 10 in' and a modulus of clasticity of E - 29 101b/in?. Using ANSYS, determine i. Deflection of each joint ii. Stress in each member Reaction forces at the base iv. Verify your results. 5 at 10 ft 13 14 11 12 15 6 9 10 ft 10 7 1000 lb 10 ft 1000 1 5 10 ft...

  • 1. Determine the forces in members DF and FE of the double-pitch roof truss shown. State...

    1. Determine the forces in members DF and FE of the double-pitch roof truss shown. State whether each of those members is in tension or compression. 2. For the given loading, determine the zero-force members in each of the truss shown. 1. Determine the forces in members DF and FE of the double-pitch roof truss shown. State whether each of those members is in tension or compression. - 4m 4m 4m 3m 3m KV 6 m 0.75 kN 6m 6...

  • A tower used in an electrical substation supports a power line which exerts a horizontal tension...

    A tower used in an electrical substation supports a power line which exerts a horizontal tension of T = 500 lb on each side truss of the tower as shown. Determine the force in members BC, CM, and LM of a side truss and indicate whether the members are in tension or compression.After a Recent cold spell, it has been seen that substantial amounts of snow and ice have accumulated on top of the structure. The top member of the...

  • Determine the force in all members of the roof truss below. State whether each member is...

    Determine the force in all members of the roof truss below. State whether each member is in tension or compression. Don't try to cram the work on this one sheet. You may use Method of Joints or Method of Sections. 1.6 m 1.6 m 1.6m 16 m 1.6 m 1.6 m 24 kN 1.2 kN 2.4 kN 2.4 kN IH 1.2 kN 2.4 K 0.9 m 1.8 18m 1.8m 1.8m 2.4m

  • a) Using the method of joints, calculate the force in each member of the trusses shown....

    a) Using the method of joints, calculate the force in each member of the trusses shown. State whether each member is in tension or compression. + L A! Lt BIC! 14m=16m- b) Determine the forces in members AC, AD, and DE. c) Determine the forces in members GI, FH, and GH. -- 5 e 3mm 15 m 60 KN

  • A tower used in an electrical substation supports a power line which exerts a horizontal tension...

    A tower used in an electrical substation supports a power line which exerts a horizontal tension of T = 500 lb on each side truss of the tower as shown. Determine the force in members BC, CM, and LM of a side truss and indicate whether the members are in tension or compression.After a Recent cold spell, it has been seen that substantial amounts of snow and ice have accumulated on top of the structure. The top member of the...

  • Problem 1 Analyze the truss structure (statically determinate) shown below. The diameter of the c...

    Problem 1 Analyze the truss structure (statically determinate) shown below. The diameter of the circular truss members is 4 cm. The material used has an elastic modulus E-160GPa 1. Calculate the forces in each truss member. 2. Calculate the horizontal and vertical displacements 1 KN of the truss nodes B and C Calculate the margin of safety. Note: Tension members can fail by stress failure and compression members can fail by stress failure or buckling. 3. 1.732 m 2 KN...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT