Question: 03 (5 Points) Varley loop test is used to find the position of an earth fault on a line of length 40km. The resistance per km of a sound cable is 28 12 and the resistance of a faulty cable is 30 2. The fixed resistor has resistance of 250 each. The fault is calculated to be 7km from the test end. To what value of resistance was the variable resistor set? (EI)