Given: 100kVA single phase transformer, Z=1.5%
Primary: 480V 2 wire
Secondary: 120/240V 3 wire
Install the above transformer to serve a branch circuit panelboard. The panelboard will be located 10' from the transformer. The primary side raceway is PVC and the secondary raceway is EMT. All calculations will conform to applicable NEC regulations. The primary side, overcurrent protection device, will be chosen based on the next available standard size of the full load amps of the transformer. The secondary side, overcurrent protection device, will be chosen based on the size of the panelboard.
Provide the following information:
1) Full load primary amps
2) Full load secondary amps
3) Standard NEMA panelboard required
4) Transformer primary protection (See specifications above)
5) Transformer secondary protection (See specifications above)
6) Primary wire size (THWN 75°C)
7) Primary equipment grounding conductor size
8) Secondary wire size (THWN 75°C)
9) Conduit size for primary feeders (Schedule 40 PVC)
10) Conduit size for secondary feeders (EMT)
11) Grounding Electrode Conductor size
12) Secondary Bonding Jumper Size
13) Available Short Circuit amps at the transformer
14) Available Short Circuit amps at the panelboard (L – L)
15) Available Short Circuit amps at the panelboard (L – N)
Given: 100kVA single phase transformer, Z=1.5% Primary: 480V 2 wire Secondary: 120/240V 3 wire Install the...
When a 15 kVA 480 primary, 120-volt secondary 2-wire secondary transformer is connected to a 11.5 kW 120-volt load, the transformer is supplying ____ amps to the load. (a.) 31.25 (B.) 54.127 (c.) 95.83 (d.) none of these
Question 31 (17 points) 120/120 single-phase transformer. Calculate the values for the equivalent circuit for the single-phase transformer for the given short and open circuit test shown below. (2 points) Draw the equivalent circuit. (1 point each) Find Ssc, QSC, Soc, Qoc, R1, R2, XI, X2, Rc, Xm, PFsc, PFoc, (esc θ。c) phase angel between V and I. What is the power rating of this transformer? Short circuit test (performed at High Voltage side) Vsc 16.20V rms, Isc 5.00 A...
The amount of available fault current at the service depends upon the ______. Method of banding Method of grounding Size and impendence of the service transformer Ampere rating of the overcurrent protection device The line current for a 240/120 volt, 3-phrase system, if each phase is balanced with a 3,000-VA load and the total load is 9,000 VA, is ______ amperes. 12.5 15 21.65 37.5 Given: A dwelling unit has 3,000 sq.ft. of habitable space with laundry facilities and bathrooms,...
answer the following multiple choice questions 5. The most common phase serving . residence would be single phase bwo or double phase three phase multiple phases none of the answers provided RV9,1110 11. A KVA code letter indicates the innush current per hp. size of the short circult protectors size of the overcurrent protectors size of the thermal overloads none of the answers provided 6. RPM is the approximate speed under full-Hoad conditions when voltage is at rated value when...
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...