NIE 2294 exam 2019.20 Aman Attya NIE 220 m Altya Question 3 NE A 100 MVA, 12.5 kV, 50-Hz, two-pole, Y-connected synchronous g

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Terminal Given that, Thermal voltage 4 = 12 ob k V Powere Factor, PF = 0.85 lagging Freequency fe = 50 Hz Syncheondus seactån(6) Internal voltage en The interenal voltage EA EA: Vo thATA tj X, IA Vo=721720° (calculated above) RA=0.01872 Scalculated aThe applied prime mover torque: Ignoscung losses, the input po were would be equal to the output power Pin = Pout - PF XS =(0

Add a comment
Know the answer?
Add Answer to:
NIE 2294 exam 2019.20 Aman Attya NIE 220 m Altya Question 3 NE A 100 MVA,...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three-phase synchronous generator with rated data VM = 20 kV, SM = 100 MVA, n...

    A three-phase synchronous generator with rated data VM = 20 kV, SM = 100 MVA, n = 500 rpm is driven by a turbine that can provide a maximum of 1.6 MNm. Synchronous reactance, XS = 3Ω / phase. The armature resistance (Ra ) is neglected. In open circuit mode (P = 0), an excitation current of 300 A is required to obtain rated voltage (VM ). The machine should be phased into a strong grid, 3x20 kV, 50 Hz....

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT