please answer all questions and show all steps
please answer all questions and show all steps 5) The voltage source V, below has a...
(10 points) In the diagram below, the source voltage phasor is V, 120L30"V (rms) and measurements show that Plant 1 receives 30kw with PF 0.9 leading, plant 2 receives 60kV A with PF 0.7 lagging and Plant 3 receives 90kW with PF 0.6 lagging. Compute the current phasor Io and the overall power factor. If the source frequency is 60H z, what single passive (time domain) component value should be added in parallel to bring the power factor to unity?...
Please show all work and concepts 5.2 (15 pts) In the following circuit, voltage source V 10020° V, 60 Hz supplies power to three load circuits with impedances Z1, Z2, and Z3. The following information was deduced from measurements performed on the three load circuits Load Z1: 45 W at pf 0.95 lagging Load Z2: 70 VA at pf 0.75 leading Load Z3: 100 VA at pf = 0.6 lagging (a) Are Z1, Z2, and Z3 inductive or capacitive? (b)...
Q5: The circuit show below has two loads connected to 120 V (rms), 60Hz, house-hold supply. The load-1 is a resistive load (lamp) with a total power of 5 kW. The load-2 is a motor drawing 10 kVA at 0.6 power factor, lagging. The capacitor is initially not connected a) Calculate the load currents (phasor) I and 12 14] b) Calculate the supply current I c) What is the power factor of the source when it supplies to both loads?...
Problem 3 Two parallel 3-phase loads are supplied from a 3-phase source with line-line voltage of 415.6922 V rms. The data of their power consumption are as follows. Load 1: 15 kVA at power factor of 0.75 lagging Load 2: 9 kW at power factor 0.82 lagging 1) 2) 3) 4) 5) Determine the complex power consumed by Load 1 Find the complex power consumed by Load 2 Calculate the total complex power consumed by the two loads. Determine the...
2. Assume the load is balanced and the source has a nositive phase sequence. If the line voltage 200 VRMS-210' operating at a frequency of 60Hz. The phase impedances Zp are based on your KSU ID as follows: Use last 6 digits of student ID number(e.g. 000123456 → 123456) Capacitor value: 100*(sum of the first three digits in microfarads) (e.g. 1+2+3 = 6 *100 = boot Inductor value: sum of the last three digits in milliHenries (e.g. 4+5+6 = 15...
Assuming that the voltage across the 10kW load has an angle of O degrees and the network has a frequency of 60Hz, please determine the following: 4. a) b) Phasor for the current in the 10kW load c) d) Phasor for the current flowing into the primary of the transformer Phasor for the current flowing in the line impedance (i.e. the 0.1? resistor and 531?? inductor). Phasor for the voltage vs Provide RMS values for all magnitudes. ?kw lo kw...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
(30) In the circuit with a voltage source and two loads below, find the following: 2. The complex power of each load a. b. The total complex power for the two loads - note units of power in the figure c. Sketch the triangle for the total complex power e total current from the source as a phasor assuming the line voltage at the load is 20820 VRMS The value of the parallel capacitance in parallel with the two loads...
5. Assuming that the voltage across the 40kW and 50kW loads has an angle of O degrees, please determine the following, using RMS values for each and assuming that the frequency is 60Hz. a) What is the real power, reactive power, and current phasor supplied by the source vs(t)1? b) Provide a phasor in RMS for the source vs(t) as well as a time-domain expression. c) Determine the total capacitance that must be placed in parallel with the two loads...