There are 300 occupants dancing in a large ballroom where a condition of 24 °C db and 60% RH is being maintained. Other heat gains are estimated as 371 kW and are all sensible. Conditioned air is supplied to the room through several registers at 14.5 °C db. The (CLF)oc.= 1.0. Calculate the followings:
(a) Total cooling load.
(b) Mass of moisture that must be removed from the ballroom per hour
The problem is solved below. Two assumptions are there that the air which is supplied is having 100% RH and mass flow rate of dry air is taken as 1 kg/s.
First sensible heat is evaluated, then latent heat is evaluated. Total heat is the sum of sensible heat, latent heat and other sensible gains. Mass of water vapour accumulated is calculated for the flow rate of 1 kg/s of dry air.
There are 300 occupants dancing in a large ballroom where a condition of 24 °C db...
PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (wet bulb) has a rate of sensible-heat gain of 25 kWand a rate of moisture gain of20 kg/hr. Moist air enters the space at a dry-bulb temperature of 15°C. Outdoor air at 35 C dB temperature and 25 C wB is supplied for ventilation purposes at a rate of 400 Us (litres per second) of standard air. After leaving the room,...
Prob. # 2] The temperature to be maintained in an office building is 26 C DB heat is 77.6 kW and the latent heat gain is 14.3 kW. Th accomplished by passing it through a spray-type heated to 18 C then supplied to the room. Find and 18 C W B. The sensible e cooling and dehumidifying of the air is washer with water chilled by refrigeration. The air is then a. the apparatus dew point temperature of washer, b....
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...