established to build, own and operate a 285 MW electricity
generating station at Al Kamil in the Sharqiya Region of the
Sultanate of Oman.The power station at Al Kamil has three
generating units. Each unit incorporates a gas turbine and an
electrical generator. One of the generators supplies 75 MW to an
infinite bus bar, the steady state limit of the system being 135
MW. Will the generator remain in synchronism if the prime mover
input is abruptly increased by 40 MW? Assume losses are zero. How
you justify your response is correct for the given scenario?
os - 135mw Here Given Data. 1 PS, 75 mw S P = 40mW New supply (Instantaneous) Ps2 = 115 mw Page No: Date: IT Area Area 2 (A2) 13 $mw-PRAY 125,=75 7 Se Se Emayr 9 op in tig, Here, If In Generator Prime mover supply (Ps) is less than electrical than (Pe) than Genenator 31) Decelerate 8 Pg > Pe than Accelerate Adcelerate A2 Decelerate Area. -TE 8 For Stability of system Decelerate Area should be more than Acceleration Area so, Az JA, Area
Date: 135 By solving So = sin' 33.74 Sc= 58.410 Smax π- Sc 180° - 58.41 1 may 121.5807 Smay is the Angle of th Deceleration An = Soffa5- 135 sins) as so 59.41 (15-135 sins) ds. 33.74° A 4. 951 units 121.58 Smax Az = f(135 sins- lis) ds ((135sins - 115) ds Se 58.41 A₂ = 14.60 Units So Clearly A₂ > Ai system will Remain in stability After Disturbance Analysis Руза Ardю. Criteria Dane from the