A three-phase Y-connected 4-pole 60-Hz synchronous generator is supplying 75 MW to a 24 kV (line-line) distribution system at a power factor 0.80 lagging. The armature phase resistance is negligible and the synchronous reactance is 2.50 ohms. The combined stray, mechanical and core losses are 1.2 MW 1. a) (3 pts) What is the line current la? b) (2 pts) What is the internal voltage Ea? c) (2 pts) What is the torque angle? d) (3 pts) What is the induced torque Tina? e) (2 pts) What is the efficiency of the generator under these conditions?

Show ALL THE FORMULAS that you use and your plugging of numbers.

Please, work the solution in an -->organized way<--, providing as much details as possible.

ANSWER ALL THE PARTS. Thank you :)