1) . A 3-phase, 400 V synchronous motor having a power consumption of 50 kW is connected in parallel with an induction motor which takes 200 kW at a power factor of 0·8 lagging.   

(i) Calculate the current drawn from the mains when the power factor of the synchronous motor is unity.

(ii) At what power factor should the synchronous motor operate so that the current drawn from the mains is minimum. ?

ANS [(i) 421 A (ii) 0·316 leading]

2) . A factory load consists of the following :

(i) an induction motor of 150 h.p. (111·9 kW) with 0·7 p.f. lagging and 80% efficiency ;

(ii) a synchronous motor of 100 h.p. (74·6 kW) with 0·85 p.f. leading at 90% efficiency

(iii) a lighting load of 50 kW.

Find the annual electric charges if the tariff is Rs 100 per annum per kVA maximum demand plus 7 paise per kWh ; assuming the load to be steady throughout the year.

ANS[Rs 1,96,070]

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
THESE ARE QUESTION FROM THE TOPIC POWER FACTOR IMPROVEMENT FROM THE SUBJECT POWER SYSTEM FUNDAMENTALS PLEASE...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A generating station supplies power to the following : (i) a lighting load of 100 kW;...

    A generating station supplies power to the following : (i) a lighting load of 100 kW; (ii) an induction motor 800 h.p. (596·8 kW) p.f. 0·8 lagging, efficiency 92%; (iii) a rotary converter giving 150 A at 400 V at an efficiency of 0·95. What must be the power factor of the rotary convertor in order that power factor of the supply station may become unity ?

  • A three-phase induction motor delivers 500 hp at an efficiency of 0.91, the operating power factor...

    A three-phase induction motor delivers 500 hp at an efficiency of 0.91, the operating power factor being 0.76 lagging. A loaded synchronous motor with a power consumption of 100 kW is connected in parallel with the induction motor. Calculate the necessary kVA and the operating power factor of the synchronous motor if the overall power factor is to be unity. Answer should be 365 kVA, 0.274

  • P3- A source supplies power to the following three load connected in parallel: (1) a light...

    P3- A source supplies power to the following three load connected in parallel: (1) a light load drawing 20 kW, (2) an induction motor drawing 10 KVA at 0.90 power factor lagging, and (3) a synchronous motor operating at 10 hp, 85% efficiency and 0.95 power factor leading (1 hp = 0.746 kW), Determine the real, reactive, and apparent power delivered by the source. Also, draw the source power triangle.

  • P3- A source supplies power to the following three load connected in parallel: (1) a light...

    P3- A source supplies power to the following three load connected in parallel: (1) a light load drawing 20 kW. (2) an induction motor drawing 10 kVA at 0.90 power factor lagging, and (3) a synchronous motor operating at 10 hp, 85% efficiency and 0.95 power factor leading (1 hp = 0.746 kW). Determine the real, reactive, and apparent power delivered by the source. Also, draw the source power triangle.

  • 1. (10 points total) A source supplies power to the following three loads connected in parallel:...

    1. (10 points total) A source supplies power to the following three loads connected in parallel: (1) a lighting load drawing 10 kW, (2) an induction motor drawing 10 kVA at 0.90 power factor lagging, and (3) a synchronous motor operating at 10 hp, 85% efficiency and 0.95 power factor leading (1 hp 0.746 kW). (a) Determine the real, reactive, and apparent power delivered by the source. (8 points)

  • please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc...

    please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc including field rheostat loss. Ans. 93.139 13.11 A generator under test is rated at 100 KVA, 3-phase, 60-Hz; 2,400 volts. (a) If driven b a de motor unexcited, the motor output is 1.26 KW. (b) If driven by a de motor, generato on open circuit and excited to generate rated potential, the motor output is 2.5 KW. ( Ifdriven by a de motor, generator...

  • Three loads are being supplied from an infinite bus operating at 400 V. Load 1 is...

    Three loads are being supplied from an infinite bus operating at 400 V. Load 1 is an induction motor consuming 50 kW at 0.7 PF lagging, Load 2 is an induction motor consuming 200 kW at 0.85 PF lagging. Load 3 is a synchronous motor whose real power consumption is 100 kW. If Load 3 is adjusted to operate at 0.8 PF leading, what is total current drawn from infinite bus by the loads?

  • Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a...

    Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...

  • 3 phase, 37.3 Kw, 440 V, 50 Hz induction motor operates at full load with efficiency...

    3 phase, 37.3 Kw, 440 V, 50 Hz induction motor operates at full load with efficiency 89% and power factor 0.85 lagging. Calculate: A) The total KVA rating of capacitor required to rise full load power factor to 0.95 lagging. B) What is capacitance per phase if capacitor: 1) Delta connected. 2) Star connected.

  • Not yet answered P Flag question Question 3 Marked out of 15.00 A 240 V source...

    Not yet answered P Flag question Question 3 Marked out of 15.00 A 240 V source energizes the parallel combination of a purely resistive 6 kW heater and an induction motor that draws 7 kVA at 0.8 lagging power factor. The overall load power factor is: Select one or more: a. pf = 0.94 (Leading) b. pf = 19.99 c. pf = 0.94 (lagging) d. pf = 0.34 (Lagging)

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT