What is/are the benefit(s) and advantage(s) of both the spinning reserve and calculating the interchange power between regions?
What is/are the disadvantage(s) of both the spinning reserve and the calculating the interchange power between regions?
A variety of reliability demands apply to the electric
utilities. Amongst others, and perhaps the most significant is that
a utility or a group of utilities must be able to accommodate the
loss of the largest generator in the system with limited power flow
and frequency variation. This generally means that all generators
on the system must have a few percent of immediate reserve capacity
associated with their rotational inertia and their primary energy
sources such as steam or hydro. Besides the fact that each
generator must run below its rated value, additional fuel is used
or water is wasted.
Thus, excess CO2 is emitted and the overall efficiency of the power
grid is reduced.
Papers as early as 1973 suggested that a large SMES system designed for diurnal use could accommodate some of a utilities’ spinning reserve requirements by installing additional power capacity into its four-quadrant ac-dc power converter. That is, the rated value of the converter would be some 20 % greater than the normal power rating of the system. The additional capacity would always be held in reserve (i.e., not used for arbitrage) and used only for in the case of loss of generation on the grid. Though the larger converter requires greater capital expenditure, because the operating temperature is somewhat reduced, it would not only provide this security, it bout be more efficient during normal operation than a device with a lower rating. At the time, no other electricity storage concept used a controllable converter and further, there was no way for the owner to accrue monetary benefits from the service.
Today, many electricity storage systems including batteries, capacitors, and flywheels interact with the grid via an electronic power controller and thus have this capability. In addition, some power markets assign high value to this functionality, allowing the owner of a facility with this characteristic to accrue monetary benefits.
The utilities generally have several reserves.
Spinning Reserve – Generation capacity that is on-line but unloaded and that can respond within 10 minutes to compensate for generation or transmission outages. “Frequency-responsive” spinning reserve responds within 10 seconds to maintain system frequency. Spinning reserves are the first type used when shortfalls occur.
Supplemental Reserve – Generation capacity that may be off-line or that is comprised of a block of “curtailable” and/or “interruptible” load and that can be available within 10 minutes. Unlike spinning reserve capacity, supplemental reserve capacity is not “synchronized” with the grid (frequency). Supplemental reserves are used after all spinning reserves are on-line.
Backup Supply – Generation that can pick up load within an hour. Its role is, essentially, a backup for reserves. Backup supply may also be used as back up for commercial energy sales.
Load Following
Load Following is required during the so-called “shoulder hours”
during the daily electric demand cycle:
While electric demand increases in the morning as people get
begin their day and get ready for work and school and other normal
daily activities, and
As electric demand diminishes in the evening as work and home
activities diminish.
As shown in Figure 1, as electric demand increases, generation
output increases to provide load following up and as demand
decreases generation output is reduced to provide load following
down.
Many utilities are experiencing a rapid development of PV generation on the distribution system. This movement is particularly prominent in islands, with the Hawaiian islands at the forefront, soon to be followed by the Caribbean. The impact of distributed PV on islands has been accelerated in two ways: the generally high price of conventional generation makes distributed PV generation cost-effective immediately, while the distributed generation has a more significant impact on a small, closed transmission system (versus the large interconnected systems on the US mainland, for example). A major consideration for the utility in terms of reliability and efficiency is the required available reserve in the presence of high PV penetrations.
Available reserves are comprised typically of two parts: spinning reserve and energy storage. The main requirement of a these reserves is that they are available to be dispatched immediately. Spinning reserves normally refers to the excess capacity of generators which are online but not operating at full capacity. Most conventional generators operate at peak efficiency at rated output. So, when the utility requires an increase in the level of spinning reserve, there is a consequential increase in the cost of meeting customer demand.
Adding a lot of distributed PV to the system increases the requirement for reserves in three key ways:
Reserves are normally required to step in when the frequency
drops rapidly (such as due to the outage of a generator). Another
thing that happens when the frequency drops is that distributed
generation will likely trip offline due to the prevailing
anti-islanding schemes on inverters. This exacerbates the drop in
frequency, so the utility must take measures (such as increasing
the available reserve) to maintain customer reliability.
PV systems can exhibit large drops in output due to a transient
event such as a cloud passing. This can result in a large drop in
output in a short space of time – a 50% drop can occur in 30
seconds. The speed of this drop in output precludes the startup of
another conventional unit, so the utility must plan for this
scenario. Where large amounts of solar power are installed in a
small area, this may have an effect on reserve requirements.
Distributed generation can impact the effectiveness of load
shedding schemes. Load shedding is employed to help arrest a drop
in frequency, as the load is reduced to help balance the available
generation. This is deployed by opening a circuit breaker and
disconnecting a specific part of the distribution system. However,
if there is distributed generation on this part of the system, the
net load dropped is less than may have been designed, reducing the
effectiveness of the load shedding scheme.
While distributed PV can be part of this problem for utilities,
they can also be part of the solution, along with some other
distributed energy sources.
Energy Storage: Energy storage, installed with PV systems or elsewhere, increases the available reserves on the system without decreasing the efficiency of conventional generators. Distributed energy storage can also be used towards this purpose, provided that a minimum discharge level is set so that some energy is always available for reserves.
Demand Response: Demand response schemes, where the load can be controlled by the utility, offer the advantages of a load shedding scheme without the disadvantages of dropping the distributed generation. They can also be useful in increasing the amount of spinning reserve in situations where demand is low by allowing the utility to dispatch more generation against the load.
Smart Inverters: Smart inverters enable the utility to randomize inverter trip points. This prevents the situation where multiple (or all) distributed PV systems trip offline at the same frequency point, which can result in a significant drop in generation and make a small outage into a system-wide blackout. Utilities can set an acceptable range of time delays for inverters to trip due to under-frequency, which results in a gradual drop in generation (and the possibility of some generation not being dropped at all). Smart inverters also offer the possibility of ceasing to energize the system, rather than disconnecting completely. This enables the inverters to re-energize the system when requested by the utility, providing that the necessary communication protocols are in place, and this can further help the system to recover.
The chart below shows an example of the system frequency following a large generator trip on systems with high penetration of distributed PV in the following cases:
No mitigation;
Energy Storage (ES);
Energy Storage with Randomized Generator Trip (ES + RGT); and
Energy Storage with Randomized Generator Trip and Demand Response
(ES + RGT + DR)
What is/are the benefit(s) and advantage(s) of both the spinning reserve and calculating the interchange power...
What is an advantage and a disadvantage of breastfeeding for both the child and the mother? What is an advantage and a disadvantage of formula bottle feeding for both the child and the mother? What may influence the choice to either breastfeed or formula bottle feed?
What are advantage(s) and disadvantage(s) of having a dominant single culture vs. a multicultural workplace in international aviation. and what would be some prevailing subculture and counterculture behaviors.
What is the advantage of considering each of the following in calculating the work done by an expanding gas? a) a massless piston b) a perfectly fitting piston
A flywheel in a motor is spinning at 540 rpm when a power failure suddenly occurs. The flywheel has mass 40.0 kg and diameter 75.0 cm . The power is off for 39.0 s , and during this time the flywheel slows down uniformly due to friction in its axle bearings. During the time the power is off, the flywheel makes 210 complete revolutions. a) At what rate is the flywheel spinning when the power comes back on? b) How...
9.16) A flywheel in a motor is spinning at 500 rpm when a power failure suddenly occurs. The flywheel has mass 40.0 kg and diameter 75.0 cm . The power is off for 39.0 s , and during this time the flywheel slows down uniformly due to friction in its axle bearings. During the time the power is off, the flywheel makes 240 complete revolutions. a. At what rate is the flywheel spinning when the power comes back on? b....
A flywheel in a motor is spinning at 500 rpm when a power failure suddenly occurs. The flywheel has mass 40.0 kg and diameter 75.0 cm . The power is off for 39.0 s , and during this time the flywheel slows down uniformly due to friction in its axle bearings. During the time the power is off, the flywheel makes 240 complete revolutions. 1. At what rate is the flywheel spinning when the power comes back on? 2. How...
what is the equation making power from spinning a generator? how that differes nuclear powerplant and convential power plant? why is it different? i need a brief explanation on these question to try understand the concept of them.
Briefly discuss an advantage of being taxed as an S-Corporation. Explain what is different from the way it would be handled if the taxpayer was a partnership or a C-Corporation. Discuss a disadvantage of being taxed as an S-Corporation. Discuss whether the advantages can outweigh the disadvantages.
Define: 1. What is Medicare Advantage? 2. What is a benefit period for Medicare? 3. Describe the 80/20 co-payment for Medicare and Medicare Advantage? 4. What is the Plan of Correction? 5. What is a deficiency? 6. What is Nursing Home Compare? 7. Describe the role of the Ombudsman? 8. Define Resident Rights? 9. What are the three therapy categories? 10. Describe Quality of Care?
A grinding wheel is spinning at a rate of 20 revolutions per second. When the power to the grinder is turned off, the grinding wheel slows with constant angular acceleration and takes 80.0 s to come to a rest. A) What was the angular acceleration of the grinding wheel as it came to rest? Should the angular acceleration be negative or postive and why?