Problem 3: The specifications of a flat-plate collector is as follows: τ = 0.88, α 0.97, U = 1.3 Btu/h ft2 °F. The heat removal factor for the collector is 0.92, the solar insolation is 210 Btu/h ft2...
Problem 3: The specifications of a flat-plate collector is as follows: τ = 0.88, α 0.97, U = 1.3 Btu/h ft2 °F. The heat removal factor for the collector is 0.92, the solar insolation is 210 Btu/h ft2, and the ambient air temperature is 60°F. Determine (a) the collector efficiency if the water enters the collector at 115°F and (b) the temperature of water at which the collector efficiency is zero. Take the incident angle modifier to be 1
Problem 3: The specifications of a flat-plate collector is as follows: τ = 0.88, α 0.97, U = 1.3 Btu/h ft2 °F. The heat removal factor for the collector is 0.92, the solar insolation is 210 Btu/h ft2, and the ambient air temperature is 60°F. Determine (a) the collector efficiency if the water enters the collector at 115°F and (b) the temperature of water at which the collector efficiency is zero. Take the incident angle modifier to be 1