Question

Question I The rating of a three phase three winding transformer are: Y-connected 10 KV 40 MVA Secondary Y-connected 22 KV 40
0 0
Add a comment Improve this question Transcribed image text
Answer #1

(110)- 202-5 = 12.10 OF 0-096_pu Xs t 10,08 XT 1、45% Equating -구·257 302-5O 057 1.06于 19.8 Kv TI 19.f 99KV teir L36-86 ST. c G4) x (2-21) 4-45JIMNA = 41,735/-17.81 41 735 MwA 99 kv

Add a comment
Know the answer?
Add Answer to:
Question I The rating of a three phase three winding transformer are: Y-connected 10 KV 40 MVA Secondary Y-connecte...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Solution of two part please with steps Question 1: Ve-le The rating of s three phase...

    Solution of two part please with steps Question 1: Ve-le The rating of s three phase three winding transformer are: Y-connected un KV 40 MVA Y-connected 22 KV 40 MVA 4 KV 15 MVA Primary Secondary Tertiary A-connected Neglecting winding resistance and exciting current, the per unit leakage reactance are X 9.6 % pu on 40 MVA. 110/22 KV X7.2 % pu on 40 MVA, 110/ 4 KV Xg 12 % pu on 40 MVA, 22 4 KV a) Determine...

  • With steps and explain please IO AS CA I PL frx-9 991ES URR 16 DATU Question...

    With steps and explain please IO AS CA I PL frx-9 991ES URR 16 DATU Question 1: The rating of a three phase three winding transformer are: Ve- llo se 4o Primary Secondary Y-connected 10 KV 40 MVA Y-connected 22 KV 40 MVA A-connected Tertiary 4 KV 15 MVA Neglecting winding resistance and exciting Xps= 9.6 % pu on 40 MVA, 110/22 KV Xpt 7.2 % pu on 40 MVA, 110/ 4 KV Xst 12 % pu on 40 MVA,...

  • The ratings of a three-phase, three-winding transformer are Y connected, 66 kV, 20 MVA Primary (1):...

    The ratings of a three-phase, three-winding transformer are Y connected, 66 kV, 20 MVA Primary (1): Secondary (2):Y connected, 13.2 kV, 15 MVA Tertiary (3): A connected, 2.3 kV, 5 MVA Neglecting winding resistances and exciting current, the per-unit leakage reactances are: X12 0.08 on a 20-MVA, 66-kV base X13 0.10 on a 20-MVA, 66-kV base X23 0.09 on a 15-MVA, 13.2-kV base (a) Determine the per-unit reactances Xi, X2, X3 of the equivalent circuit on a 20- MVA, 66-kV...

  • three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit...

    three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...

  • Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary...

    Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary Voltage Excitation reactance Series Impedance 150 MVA 230 kV 32 kV 30 (pu) 0.02+0.15j (pu) The transformer is Y/A connected. Answer the following questions: a) What are the nominal (rated) primary and secondary line currents?| b) What is the nominal value of the Delta-side winding (internal) current? c) What is the secondary to primary winding turn ratio? d) The transformer is supplying 150 MVA...

  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...

  • A generator transformer has a magnetising current of 1.5 %. The primary winding voltage is 27 kV and the secondary voltage is 330kV. The transformer rating is 360 MVA. What is the allowable operating...

    A generator transformer has a magnetising current of 1.5 %. The primary winding voltage is 27 kV and the secondary voltage is 330kV. The transformer rating is 360 MVA. What is the allowable operating current differential, in terms of Amperes on the primary, that should not cause the protection to operate? Select one: a. 200.00 Amperes b. 31.08 Amperes c. 115.47 Amperes d. 66.00 Amperes

  • Problem 3. A three-phase transformer is constructed using three single-phase two-winding trans- formers, each has the...

    Problem 3. A three-phase transformer is constructed using three single-phase two-winding trans- formers, each has the same ratings of 500 MVA, 15/240 kV, and leakage impedance of XT.p.u 0.2 p.u The high-voltage side of the three-phase transformer is connected to a three-phase Y-connected load that absorbs 1000 MVA at 0.9 power factor (lagging). The phase-a voltage across the load is Van 2402(0) kV. Answer the following questions. [10 points] a) Calculate the phase-a voltage at the low-voltage side (denoted by...

  • QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase...

    QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase reactance Xg of 1.5 pu and supplies 0.8 pu per phase real power (P) at the rated voltage, with a lagging power factor of 0.6 to the load. Find the actual excitation voltage Vo in kV (line value). 96.392