Question

A sample system consists of three generation units. Table 1 shows the corresponding generation system data, while Table 2 des
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solution:

Capacity Outage Probability Table a. Given that the probability of unit failure is assumed to be 0.02 i:e U-0.02 Therefore P(Here I done solution by taking the average of all quantities it is not mentioned that to be done for individual or average. CELL for 1 1.12MW = 1120 kW ELL for 2 0.0224MW = 22.4 kW LOLP-0.02 LOLE 0.02 365 = 7.3d/yr LOLP 0.0004 LOLE 0.0004*365=0.146d/