0% 0 pts) A 100 kVA. I 3 8 2.4 kV step down transformer has the following parameters (referred to the secondary): Rop-0.08 04m Tn the transformer is 100 ad KVA at 09 pf lagging at 2160 V. Find the voltage applied to the primary side of the transtormer Find the voltage regulation and efficiency 216D Q니 10.3-2400 1002 042to V(52 467 oo62 06 (10 pts) Solve the previous problem using the PU system. Use the rating of the transformer as base values5
0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
0% 0 pts) A 100 kVA. I 3 8 2.4 kV step down transformer has the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a...

    4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a feeder with impedance of 100/60° Ω Load 90 kw 0.85 PF lagging Feeder transmission line) Source Transformer Load The transformer has been tested to determine its equivalent circuit. The results of the tests are: Open-circuit test Voc = 14 kV oc 0.1 A Рос-800 w Short-circuit test Vsc 800 V Isc = 7A Psc 2 kW The load on the transformer is 90 kW...

  • A three phase power transformer of 100 (KVA), 22 / 12.7 (kV) and Δ-Y has a...

    A three phase power transformer of 100 (KVA), 22 / 12.7 (kV) and Δ-Y has a resistance of 0.15 (pu) and a reactance of 0.6 (pu). The elements of the excitation branch are R_m = 100 (pu) and X_m = 20 (pu) a) If this transformer supplies a load of 80 (KVA) with an FP = 0.8 delay, draw the phasor diagram of one phase of the transformer. b) What is the voltage regulation of the transformer bank in these...

  • 1) A single-phase 50-kVA, 2400/240 volt, 60 Hz distribution transformer is used as a step-down tr...

    1) A single-phase 50-kVA, 2400/240 volt, 60 Hz distribution transformer is used as a step-down transformer at the load end of a 2400-volt feeder whose series impedance is (1.0+2.0) Ω. The equivalent series impedance of the transformer is (10+j25) Ω referred to the high voltage (primary) side. The transformer is delivering rated load at 0.8 power factor lagging and at rated secondary volitage. Neglect the transformer exciting curent. Using the transtormer raltings as base quantities work this problem in per...

  • Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp...

    Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp 322 X,-45 Ω R,-0.05 Ω X,-0.06 Ω The excitation branch impedances are given referred to the high-voltage side of the transformer. (a) Find the equivalent circuit of this transformer referred to the high-voltage side. (b) Assume that this transformer is supplying rated load (20kVA) at 480 V and 0.8 PF lagging. What is this transformer's input voltage? What is its voltage regulation? (c) What is the transformer's...

  • A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which...

    A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary voltage. b) load impedance. c) load impedance referred to the primary. d) the real and reactive power supplied to the primary winding

  • 3.4 A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load,...

    3.4 A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary wind- ing, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: (a) primary voltage, (b) load impedance, (c) load impedance referred to the primary, and (d) the real and reactive power sup- plied to the primary winding.

  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

  • lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. De...

    lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...

  • A power transformer has rated power of 100 KVA and rated primary voltage of 22 KV....

    A power transformer has rated power of 100 KVA and rated primary voltage of 22 KV. The series impedance is given as 1 + 15% pu. Find the series impedance in ohms.

  • Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of thr...

    please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...