Question

A heat pump using refrigerant-134a as a refrigerant operates its condenser at 800 kPa and its...

A heat pump using refrigerant-134a as a refrigerant operates its condenser at 800 kPa and its evaporator at −1.25°C. It operates on the ideal vapor-compression refrigeration cycle. What is the COP of the heat pump for the case when the vapor entering the compressor is superheated by 2°C and for the case when the compressor has no irreversibilities?

The COP of the heat pump when the compressor has no irreversibilities is____.

The COP of the heat pump when the vapor entering the compressor is superheated by 2°C is ____.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

clami Jala Drawing the Ts diagram of the cycle. Obtaining data at each state. TA / 900 kPa State ♡:- P, = 280kla Tho - 251op of heat pump when the compressor has no trreversibilitied! - 271-50 - 95-47 Cop - h2s - 3 has-hi 271.CO - 249.72 Op = 8.0

Add a comment
Know the answer?
Add Answer to:
A heat pump using refrigerant-134a as a refrigerant operates its condenser at 800 kPa and its...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression cycle....

    (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression cycle. The cycle operates between 200 kPa and 1.2 MPa. The refrigerant flows through the cycle at a rate of 0.019 kg/s. The (actual) refrigerator has a compressor with an isentropic efficiency of 85%. The refrigerant enters the compressor slightly superheated by 56 C hint add this to the saturation temperature). The refrigerant leaves the condenser slightly subcooled by 1.9°C. What is the rate of...

  • Tt (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression...

    Tt (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression cycle. The cycle operates between 200 kPa and 1.2 MPa. The refrigerant flows through the cycle at a rate of 0.015 kg/s. The actual) refrigerator has a compressor with an isentropic efficiency of 82%. The refrigerant enters the compressor slightly superheated by 6.2°C (hint: add this to the saturation temperature). The refrigerant leaves the condenser slightly subcooled by 1.8°C. What is the rate of...

  • QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is...

    QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is used to heat water from 15°C to 45°C at a rate of 0.12 kg/s. the condenser and evaporator pressures are 1.4 and 0.32 MPa, respectively Determine: (a) The power input to the heat pump QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is used to heat water from 15°C to 45°C at a rate of 0.12 kg/s....

  • Refrigerant-134a enters the condenser of a residential heat pump at 800 kPa and 35°C at a...

    Refrigerant-134a enters the condenser of a residential heat pump at 800 kPa and 35°C at a rate of 0.018 kg/s and leaves at 800 kPa as a saturated liquid. If the compressor consumes 1.2 kW of power, determine (a) the COP of the heat pump and (b) the rate of heat absorption from the outside air.

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34°C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat transfer...

  • Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C...

    Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C at a rate of 0.025 kg/s and leaves at 1000 kPa as saturated liquid. If the compressor consumes 2 kW of power, determine: a) The COP of the heat pump (as heating device). b) The rate of heat absorption from the outside air. тан Condenser Throttling valve Compressor Evaporator To

  • An ideal vapor-compression refrigeration cycle that uses refrigerant R-134a as its working fluid maintains a condenser...

    An ideal vapor-compression refrigeration cycle that uses refrigerant R-134a as its working fluid maintains a condenser at 800 kPa and the evaporator at -12C. (a) Determine this system's COP and the amount of power required to service a 150kW cooling load. (b) Determine the P,T, h, S and exergy of R-134a at all four states of the entire cycle. Assume the ambient temperature to be 25C.

  • A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid....

    A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid. Superheated vapor enters the compressor at 10 lbf/in2 , 0 oF. The liquid leaving the condenser is at 180 lbf/in2 , 100 oF. There is no significant pressure drop in the evaporator or condenser. For compressor efficiency of 83% and refrigeration capacity of 6 tons, determine (a) the compressor power input in horsepower, and (b) the coefficient of performance. A vapor compression refrigeration system...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT