Determine the required footing thickness and design the reinforcement for the combined foot ing shown in...
A 16-in square concrete column carries vertical unfactored load of 350 k factored load. It is to be supported on a 8'square footing with fc=3000 lb/in2 and fy-60 k/in2. The groundwater table is at a great depth. Because of frost heave considerations, the bottom of this footing must be at least 30 inches below the ground surface. Determine the required footing width thickness, size the flexural reinforcement, and show your design in a sketch ASD standards: allowable bearing capacity 6,500...
In the figure shown a square footing 3m x 3m has a thickness, h= 600mm and effective depth, d= 530mm. The concrete compressive strength, f = 28MPa and the reinforcing steel yield strength, f = 420MPa. The footing carries a rectangular column of 40 cm x 60 cm. Check the adequacy of the footing to carry an axial dead load of 1200 kN and an axial live load of 1600 kN based on shear strength requirements. 3 m 60 cm...
CVE 313- 1- Design a square footing for the interior column shown in the figure. The column carries 2 k 't of uniform live load and 1.5 k/t of uniform dead load (including the self weiht of the structure), the base of the footing is 5 ft below grade, the soil weight is 100 lb/ft', and q," 5000 psf. and concrete unit weight is 150 lb/ (25 points) NOTE: Your design should only include the following (one-way shear, two-way shear,...
Part-I: OPEN BOOK Problem 1 (30 points). For the isolated square footing shown below, assume that the combined weight of soil and concrete above the base of the footing is equal to 120 pcf. Assume fc-3000 psf and column size of 18in. x 18 in. Determine the followings: a) If the footing size of 10ft. x10ftx 2ft. is adequate based on allowable soil-bearing capacity qa 6,000 psf b) If the footing 10ft. x10ft.x 2ft. is adequate for shear e) Calculate...
. Deisgn a reinforced concrete cross-section with unknown dimensions Problem 1 Design the steel reinforcement for the beam shown in Figure 1 that supports its own self-weight, a uninformly distributed dead load, a uniformly distributed live load, and a live point load located at midspan. In your solution, you should select the area of reinforcement, the number and size of reinforcing bars, and the section depth in order to receive full credit. Assume J 5,000 psi, fy 60,000 psi. 16...
S. Al-Martini, PhD, P. Eng. Question No. 5 (35minutes) 19 marks) As shown in the figure, a 9-ft 6-in square footing supporting an 18-in. -square tied concrete column and it is subjected to service dead load 225 kips, and service live load 175 kips. column is a typical interior column in a building. Assume normal-weight concrete.. soil pressure (ga) 5000 psf (5 ksf), f'e for column 4000 psi, f's for the footing lsteel 60, 000 psi. The density of the...
S. Al-Martini, PhD, P. Eng. Question No. 5 (35minutes) 19 marks) As shown in the figure, a 9-ft 6-in square footing supporting an 18-in. -square tied concrete column and it is subjected to service dead load 225 kips, and service live load 175 kips. column is a typical interior column in a building. Assume normal-weight concrete.. soil pressure (ga) 5000 psf (5 ksf), f'e for column 4000 psi, f's for the footing lsteel 60, 000 psi. The density of the...
2. Design a rectangular section for the beam below with the loads shown. The self weight of the beam is not included in the dead load of the beam and should be considered in the design. Show a sketch of your cross section, including bar sizes, arrangement, and spacing. Assume concrete weighs 150 lb/ft. Use Grade 50 steel with f 3,000 psi Use a target ρ-0.18 (/f, PD = 15 k PL = 10 k 2 k/ft (excludes beam weight)...
Problem 1 Reinforced Concrete T-Flanged Sections (50 pts.) You are required to analyze and design the propped cantilever t-section from HM 4 but for shear only. Draw shear V and moment M diagrams for uniformly distributed load throughout the 30ft span and equally concentrated loads at 10ft and 30ft. Recall that the connection at the left joint N1 is fixed. The connection at 20ft N3 is a roller. The right end node N2 is a free end. Usea concrete compressive...
reinforced concrete design Problem 2: Design of T-beam Calculate the reinforcing required for the T-beam system below 22 30 15 15 10'0 10'0 10 0 1 of 2 live load is 400 lbf/ft2 and use the dimensions shown in the figure. (a) Calculate the maximum factored moment (note: remember to include the self-weight of slab and beams) (b) Determine the effective flange width (c) Check if a