Given:
Span=10 ft
hf=8 in
d=22 in
L.L=400 lb/ft2
Self weight of slab=(8 in/12x150) lb/ft3
D.L of slab=100 psf
effective flange width=span/4=60 in(assume it is least)
Area of beam=8*60+22*15=810 in2
D.L of beam=810x150/144=843.75 psf
(a)
Wu=1.2(D.L)+1.6(L.L)
Wu=1.2(843.75)+1.6(400)
Wu=1652.5 psf
M=WL2/8
M=1.6525x(20)2/8
M=82.625 ft-kips
(b)
Effective flange width
Span/4=20x12/4=60 in
16hf+bw=16x8+15=143 in
spacing=120 in
The effective flange width is 60 in
(c)
Mn=M/()
Mn=82.625/0.9=91.8 ft-kips
Assume a lever arm of z=0.9d or z=d-hf/2
z=0.90x22=19.8 or z=22-8/2=18 in
AsFyZ=Mn
As=91.8x12/(60x19.8)
As=0.92 in2, which is less than the minimum area of steel
Provide 2 no of #10 bars of area 2.53 in2
equate the tension to compression
0.85fcAc=AsFy
0.85x4xAc=2.53x60
Ac=44.64<240 in2
a=44.64/60
a=0.74<hf
The minimum steel is 1.1 sq in providing 2.53 sq in of #10 no of 2 bars will be enough and a<hf
(e)
c=0.74/0.85
c=0.87 in
t=0.072>0.005
The reduction factor is 0.9
(f)
Assume the cover of concrete to the T beam as 1.5 in. select a #4 diameter stirrup
Check the spacing
S=[bw-2(clear cover)-0.5(diameter of stirrup)-0.5(diameter of bar)]/2
S=[15-2(1.5)-0.5(0.5)-0.5(1.25)]/2
S=5.5 in
Sketch:
(g)
Moment capacity=0.90TZ
=0.90AsFy(d-a/2)
=0.90x2.53x60x(22-0.74/2)/12
=246.25 ft-kips>91.1 ft kips, this is safe
Problem 2: Design of T-beam Calculate the reinforcing required for the T-beam system below 22 30 ...
A floor system (Figure 2) consists of a 3 in. concrete slab supported by continuous T beams with a span L=24 ft, and 47 in. on centers distance between beams. Web dimensions, as determined by the negative-moment requirements at the supports are bw=11 in. and d=20 in. Use concrete clear cover of 2 in. Determine the tensile steel of the T-beam that is required at mid-span to resist a factored positive moment of Mu=530 kip-ft if fc’=3,000 psi and fy=60,000...
please help with this problem Problem Statement You are asked to design an exterior balcony for a client. The client has a 7,000 sq ft 2-story house. He wanted to add a nice looking balcony to it. He showed you the rough sketches and dimensions. The balcony is to be supported on two simply-supported edge beams. Each beam is supported by two short columns, each column is supported by appropriate footings. is! slao - beams Supporting slab Columns supporting beans...
no please Problem (2): Given: As an engineer, you have been asked to design a reinforced concrete floor system consists of a 5-in concrete slab supported by T-beams of 24-ft spans. The T-beams are spaced 4 ft and bw (width of the beam part 15". Total height is 25 inches. If you try to find the steel required for T-beam for moment due to Mp- 500 ft-kips and M-300 ft-kips, what would be the type of T-Beam (Regular or True...
1. T-Beams are used to support a floor in an industrial building. The floor is used for product storage so it must be designed for a heavy 600 psf. The floor must also support a superimposed dead load of 20 psf (in addition to the self-weight of the beams and slab. The layout of the beams and slabs is shown below. The beams span 30.0% and are spaced at 4.0” center to center. The slab is 3” thick. The concrete...
Design a 24-in.-wide precast concrete slab to support a 60-psf live load for a simple span of 15 ft. Assume the minimum concrete cover required to be 5 in. Use welded wire fabric for reinforcing steel. J.-б0,000 psi,//-3000 ps, and ρ = 0.18/ 'My (Ans. 4-in. slab with 4 × 8 D12/D6) Design a 24-in.-wide precast concrete slab to support a 60-psf live load for a simple span of 15 ft. Assume the minimum concrete cover required to be 5...
b.323 The empirical provisions of 6.3.2.1 and 6.3.2.2 were developed for nonprestressed T-beams. The flange widths in 6.3.2.1 and 6.3.22 should be uset Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-wav slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly...
Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-way slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly distributed, factored load of 5 k/ft. (b) Design the slab reinforcement for the positive moment region using a factored load of 500 psf....
reinforced concrete design , ACI code Shear Strength of Flexural Members Design for shear forces The simply supported beam shown is subjected to ultimate (factored) distributed and concentrated loads 1. Determine the shear capacity of concrete at the critical section according to ACI318-14 detailed method in Table 22.5.5.1. Design the shear reinforcement and determine the locations on the beam shear force diagram where this shear reinforcement should be placed. 2. 3. Determine the locations within the beam where minimum shear...
Problem 1 Reinforced Concrete T-Flanged Sections (50 pts.) You are required to analyze and design the propped cantilever t-section from HM 4 but for shear only. Draw shear V and moment M diagrams for uniformly distributed load throughout the 30ft span and equally concentrated loads at 10ft and 30ft. Recall that the connection at the left joint N1 is fixed. The connection at 20ft N3 is a roller. The right end node N2 is a free end. Use a concrete...
Problem 1 Reinforced Concrete T-Flanged Sections (50 pts.) You are required to analyze and design the propped cantilever t-section from HM 4 but for shear only. Draw shear V and moment M diagrams for uniformly distributed load throughout the 30ft span and equally concentrated loads at 10ft and 30ft. Recall that the connection at the left joint N1 is fixed. The connection at 20ft N3 is a roller. The right end node N2 is a free end. Usea concrete compressive...