Question

Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 895 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected.

a)Determine the mass flow rate of the dry air in lb(dry air)/min.

b)the relative humidity at the exit

c)the dew point temperature at the exit

0 0
Add a comment Improve this question Transcribed image text
Answer #1

2 95 F DBT Mank state u» psychrometoc chcat using Diaw constant enlhalpy line 1-2 bill T2 = 15F mank staka point 2. (aFom ps

Add a comment
Know the answer?
Add Answer to:
Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in lbm(dry...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in Ibm(dry...

  • Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating...

    Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. Using data from the psychrometric chart, determine: (a) the humidity ratio of the entering moist air mixture, in kg(vapor) per kg(dry air). (b)...

  • Moist air at 30°C, 1 atm, and 42% relative humidity enters an evaporative cooling unit operating...

    Moist air at 30°C, 1 atm, and 42% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. A. Determine the specific humidity of the entering moist air (to the heating section). (5 of 45 points. Please input your final answer...

  • 12.54 Air at 12°C, 1 atm, and 40% relative humidity enters a heat exchanger with a...

    12.54 Air at 12°C, 1 atm, and 40% relative humidity enters a heat exchanger with a volumetric flow rate of 1 m'/s. A separate stream of dry air enters at 280°C, 1 atm with a mass flow rate of 0.875 kg/s and exits at 220°C. Neglecting heat transfer between the heat exchanger and its surroundings, pressure drops of ach stream, and kinetic and potential energy effects, determine (a) the temperature of the exiting moist air, in °C

  • Moist air enters a duct at 10 °C, 80% relative humidity, and a volumetric flow rate...

    Moist air enters a duct at 10 °C, 80% relative humidity, and a volumetric flow rate of 150 m3/min. The mixture is heated as it flows through the duct and exits at 30 °C. No moisture is added or removed and the mixture stays at 1 atm. Determine the rate of heat transfer and the relative humidity at the exit.

  • Moist air at 20°C, 1 atm, and 43% relative humidity and a volumetric flow rate of...

    Moist air at 20°C, 1 atm, and 43% relative humidity and a volumetric flow rate of 900 m/hrs. enters a control volume at steady state and flow along a surface maintained at 65° C, through which heat transfer occurs. Liquid water at 20° C is injected at a rate of 5 kg/hr and evaporates into flowing stream. For the control volume, Wev =0, and kinetic and potential energy effects are negligible. Moist air exits at 32°C, 1 atm. (a) draw...

  • Moist air at 20° c, 1 atm, and 43% relative humidity and a volumetric flow rate...

    Moist air at 20° c, 1 atm, and 43% relative humidity and a volumetric flow rate of 900 m/hrs. enters a control volume at steady state and flow along a surface maintained at 65 C, through which heat transfer occurs. Liquid water at 20" C is injected at a rate of 5 kg/hr and evaporates into flowing stream. For the control volume, Wa=0, and kinetic and potential energy effects are negligible. Moist air exits at 32c, 1 atm, (a) draw...

  • Moist air at 20°C, 1 atm, and 43% relative humidity and a volumetric flow rate of...

    Moist air at 20°C, 1 atm, and 43% relative humidity and a volumetric flow rate of 900 m²/hrs. enters a control volume at steady state and flow along a surface maintained at 65°C, through which heat transfer occurs. Liquid water at 20°C is injected at a rate of 5 kg/hr and evaporates into flowing stream. For the control volume, Wev=0, and kinetic and potential energy effects are negligible. Moist air exits at 32°C, 1 atm. (a) draw the system schematic...

  • Example 5: Ambient air at 38°C db-temperature and 20°C wb- temperature enters an evaporative cooler with...

    Example 5: Ambient air at 38°C db-temperature and 20°C wb- temperature enters an evaporative cooler with a dry air mass flow rate of 0.75 kg/s. The pressure is constant at 95 kPa. The air leaves at a db-temperature of 25°C. Calculate (i) the relative humidity of the air at inlet, (ii) the relative humidity of the air at exit, (iii) the rate of flow of water to the cooler, and (iv) the saturation effectiveness of the cooler.