voltage at which power is provided to the city=50*10=500 kV
power to be sent=230 MW
current=power/voltage=230*10^6/(500*10^3)=460 A
total loss=0.04*230 MW=9.2*10^6 W
then resistance required=loss/current^2
=43.478 ohms
total length=120+120=240 km=240000 m
as resistance=resistivity*length/area
==>43.478=1.68*10^(-8)*240000/area
==>area=1.68*10^(-8)*240000/43.478=9.2737*10^(-5) m^2
==>pi*(diameter/2)^2=9.2737*10^(-5)
==>diameter=sqrt(4*9.2737*10^(-5)/pi)=0.010866 m
=1.0866 cm
An electric power station that operates at 50 kV and uses a 10:1 step-up ideal transformer...
An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 260 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.68 × 10^ -8 Ω.m). What is the diameter of the wires?
An electric power station that operates at 20 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 230 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 x 10^-8 Ω.m). What is the diameter of the wires? ANSWER IN CM.
An electric power station that operates at 30 kV and uses a 20:1 step-up ideal transformer is producing 330 MW (Mega-Watt) of power that is to be sent to a big city which is located 300 km away with only 2.5% loss. Each of the two wires are made of copper (resistivity = 1.68 × 10 − 8 Ω.m). What is the diameter of the wires? Please show detailed work!
An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer is producing 390 MW (Mega-Watt) of power that is to be sent to a big city which is located 230 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires? Answer in cm. 0.05395 isn't correct.
An electric power station that operates at 10 kV and uses a 10:1 step-up ideal transformer is producing 330 MW (Mega-Watt) of power that is to be sent to a big city which is located 290 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires?
An electric power station that operates at 10 kV and uses a 20:1 step-up ideal transformer is producing 380 MW (Mega-Watt) of power that is to be sent to a big city which is located 210 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = Ω.m). What is the diameter of the wires? ANSWER IN cm
An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer is producing 370 MW (Mega-Watt) of power that is to be sent to a big city which is located 260 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.72×10−81.72×10−8 Ω.m). What is the diameter of the wires?
An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer is producing 340 MW (Mega-Watt) of power that is to be sent to a big city which is located 220 km away with only 3.0% loss. Each of the two wires are made of copper (resistivity =1.72*10-8 Ω.m). What is the diameter of the wires? _________ cm
An electric power station that operates at 25 kV and uses a 15:1 step-up ideal transformer is producing 350 MW (Mega-Watt) of power that is to be sent to a big city which is located 240 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires?
10. An electric power station that operates at 25 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 230 km away with only 3.0% loss. Each of the two wires are made of copper (resistivity = 1.72 x 10-8 2.m). What is the diameter of the wires? x 3.90 cm Show my other submissions)