Question

This experiment will give information regarding the behavior of the MUT induction machine under full load...

This experiment will give information regarding the behavior of the MUT induction machine under full load conditions. In this experiment, rather than having a separate mechanical load for the MUT induction machine, the VSD controlled induction machine will act as a mechanical load. The VSD induction machine will act in torque control mode to ensure that a counteracting full load torque is applied to the MUT induction motor. It's rated at 5.5kW. When the motor deliver rated power output, if it connected to a 660V (VLL) voltage, it will draw 6.2A at 0.886 lagging power factor. If the supplied frequency is 50 Hz, its full load mechanical speed is 1460 r.p.m.

VLL = 422 V
IL = 13.6 A
pf = 0.830
Motor speed = -1470 rpm

a)What is the real power being delivered to the machine in this test?
b)What is the reactive power being delivered to the machine in this test?
c)Using the cantilever (approximate) equivalent circuit, determine the output power delivered by the MUT induction machine.
d) What is the machine efficiency?
e) Determine the electrical and mechanical torque.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

a.) Real power being delivered to machine in the test=P =V3ViIL cos

Given, during test: Line voltage=422V; Line current =13.6A; pf= \cos\phi =0.830

P = 8250.44 W or 8.25 kW

b.) Reactive power being delivered to machine in the test=Q =\sqrt{3}V_LI_L\sin\phi

Using other values same as in above part,\sin\phi=\sqrt{1-\cos^2\phi}=\sqrt{1-(0.83)^2}=0.558

Q = 5546.68 W or 5.55 kW

c.) The data is given for two voltages in the quesion:

1.Rated: Line voltage=660V; Line current =6.2A; pf= \cos\phi =0.886, n_1 =1460 r.p.m., P_{rated} =5.5kW, Torque, T_1

T_1=\frac{P_{rated} }{2\pi n}=35.99 N-m

2.Test: Line voltage=422V; Line current =13.6A; pf= \cos\phi =0.830, n_2 =-1470r.p.m., P_{out} , T_2

Since, the motor is being operated in torque control region and we know that:T\propto V^2.

So, we can find Torque during test as follows:

\frac{T_2}{T_1}= \frac{V_2^2}{V_1^2}\Rightarrow T_2=\frac{422^2}{660^2}\times 35.99=14.71Nm

P_{out}= T_2w_2=14.71\times \frac{1470}{60}\times 2\pi =2.263kW

d.)\eta=\frac{Output Power}{Input Power}\times 100=\frac{2.263}{8.25}\times 100=27.4\%(During test)

Under rated conditions:

\eta=\frac{Output Power}{Input Power}\times 100=\frac{5500}{\sqrt{3}\times660\times 6.2\times 0.886}\times 100=89.6\%(Under rated conditions)

Hope you find the answer helpful. You can comment if you have any doubts.

Your feedback help us perform better. Please rate the answer if it was helpful to you.

Thanks! Keep questioning.

Add a comment
Know the answer?
Add Answer to:
This experiment will give information regarding the behavior of the MUT induction machine under full load...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 240-V, 20hp, four poles, 50 Hz, Y-connected induction motor has a full-load slip of 2...

    A 240-V, 20hp, four poles, 50 Hz, Y-connected induction motor has a full-load slip of 2 percent. What is the rotor speed of this motor at rated load? 1470 rpm 1420 rpm 1500 rpm 1400 rpm

  • 4.6. A 460-V, 75 kW, 4-pole, delta-connected, 60-Hz, three- phase induction motor has a full-load slip of 5 percent, an efficiency of 92 percent and a power-factor of 0.87 lagging at full-load. At st...

    4.6. A 460-V, 75 kW, 4-pole, delta-connected, 60-Hz, three- phase induction motor has a full-load slip of 5 percent, an efficiency of 92 percent and a power-factor of 0.87 lagging at full-load. At start-up, the motor develops 1.9 times the full load developed torque but draws 7.5 times the rated current at the rated voltage. This motor is to be started with an auto- transformer reduced-voltage starter. Assume the stator resistance and the stator core loss to be negligible. Calculate...

  • For a 6-pole, 2-phase squirrel-cage induction machine, the following parameters are given: 10, .is . Žml,...

    For a 6-pole, 2-phase squirrel-cage induction machine, the following parameters are given: 10, .is . Žml, .mas : 1 BrnII,? 0.5?, l?r 1mil The induction machine works as a motor being supplied by a 60-Hz source. The rotor speed is ar360 rads In his ip of operaion, s1A1. A; 25.1/1/1.9° A, calculate the following (i) Electromagnetic torque (6') (ii) Rotor copper loss due to the rotor winding resistance (5') (ii) Mechanical power delivered to the load. (6') Determine Vas, las,...

  • A 2-pole, 20MW single phase induction machine used for driving a train has a slip of...

    A 2-pole, 20MW single phase induction machine used for driving a train has a slip of 4.12%, when it is delivering 80% of its rated torque and 15.6MW. The rotor speed at the rated torque/power is 3415 rpm. (i) Determine the synchronous speed of the motor, under the above conditions, as well as the frequency required by the power electronics in the drive (ii) If the torque and synchronous speed were kept constant under the above conditions, calculate the load...

  • A three-phase, 50-Hz, 4-pole, 575-V (line-line, rms) induction motor drive has a full-load (rated) speed of...

    A three-phase, 50-Hz, 4-pole, 575-V (line-line, rms) induction motor drive has a full-load (rated) speed of 1450 rpm. The rated torque is 50 Nm. Keeping the air gap flux-density peak constant at its rated value, (a) plot the torque-speed characteristics (the linear portion) for the following values of the frequency: 50 Hz, 40 Hz, 30 Hz and 20 Hz. (b) This motor is supplying a load whose torque demand increases linearly with speed such that it equals the rated motor...

  • 60Hz, 380V, 4 pole 30kW induction motor, When its driving under full load condition, the speed...

    60Hz, 380V, 4 pole 30kW induction motor, When its driving under full load condition, the speed is 1746rpm, input current 56.2A power factor 90%. Under no-load condition, input current 17.3A, power factor 13.5%. (In full load operation, assume that the mechanical loss is 25% of the total loss and no other losses.) a) Efficiency under full load b) Find a rotor copper loss under full load c) Core loss d) Find a fixed stator copper loss under full load e)...

  • 7. A 3-phase, 300 kW, 2300 V, 60 Hz, 1800 r/min induction motor is used to...

    7. A 3-phase, 300 kW, 2300 V, 60 Hz, 1800 r/min induction motor is used to drive a compressor. The motor has a full- load efficiency and power factor of 93 percent and 87 percent, respectively. If the terminal voltage rises to 2750 V while the motor operates at full-load, determine the effect (increase or decrease) upon a. Mechanical power delivered by the motor b. Motor torque c. Rotational speed d. Full-load current e. Power factor and efficiency f. Starting...

  • A two-pole, 75kW, 440 V, 50 Hz, Y-connected, three-phase squirrel cage induction motor has the fo...

    Please solve this question. Thank you. A two-pole, 75kW, 440 V, 50 Hz, Y-connected, three-phase squirrel cage induction motor has the following parameters, in Ω/phase referred to the stator: R1-0.075, XI 0.17, xm-72, R2-0.065 and X-0.17. Its rated slip is 4%. Assume that the mechanical losses are 1 kW and the core losses are 1.1 kW. Compute: a. The rated input current b. The rated power factor. c. The pullout torque d. The induced and load torques at rated conditions....

  • The three-phase wye-connected induction motor nameplate gives the following information: 400 V, 1755 rpm, 60 Hz....

    The three-phase wye-connected induction motor nameplate gives the following information: 400 V, 1755 rpm, 60 Hz. Rotor speed at no-load is 1799 rpm. At rated voltage and frequency motor core losses are 400 W. At rated rotor speed, mechanical losses are 400 W. The available parameters of the motor conventional equivalent circuit (6-parameters IEEE model) are: R1 = 0.2 Ω, R’2 = 0.2 Ω, X1 = 0.5 Ω, X’2 = 0.2 Ω and Xφ = 20.0 Ω. In all calculations,...

  • A three phase induction motor draws a starting current which is five times the full load...

    A three phase induction motor draws a starting current which is five times the full load current with direct on line starting, while developing twice the full load torque. Q2.1. Based on the two facts that starting current is proportional to the applied voltage and that the starting torque is proportional to the square of the applied voltage, determine voltage (as a per cent of rated voltage) required to obtain a starting torque equalling the full load torque. (10 marks)...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT