Given data:-
Beam effective depth (d) = 18"
Beam width (b) = 14"
Area of steel (As) = 4.68 in2
f'c = 5 ksi
fy = 75 ksi
Determine :- Cracked moment of inertia
Assumed modular ratio (n) = 9
We know that location of neutral axis of singly reinforced beam is given by as
----------------------------------Eq.1
Put all knowing data in Eq.1
Solving above equation and calculeting location of neutral axis (x)
Location of neutral axis (x) = 7.82 inch
Cracked moment of inertia of singly reinforced beam is given by
---------------------------------------Eq.2
Where b = 14"
n =9
As= 4.68 in2
x = 7.82 inch
d = 18"
Put all data in Eq.2
Ans.
Problem 3 (30 points) compute the cracked moment of inertia, Ic, of the beam shown below....
Cracking Moment (Uncracked Concrete Stage) Problem 1) Problem 2.6 (page 55, McCormac and Brown, gth Ed.) Note: Modify the total depth of the beam from 24" to 26" and the depth of the steel rebars from 21" to 23". Transformed Area Method (Concrete Cracked- Elastic Stresses Stage) Problem 2) Problem 2.13 (page 56, McCormac and Brown, 8th Ed.) Note: Make the following changes: Change fe to 5 ksi use the values and dimensions shown in the figure below 1) 2)...
Example SW-11 Determine the design moment capacity for the T-beam floor system shown The beam has four #9 tension bars. Assume a clear span of 21 ft-3 in. fe 4000 psi, and fy 60 ksi be d-13%" 64%"
Problem 2 For the area method to compute ratio (n) is equal to 8 beam cross section shown below, assume the section has cracked. Use the transformed- the flexural stresses for the moment value of 60 k-ft and the modular 17 in 20 in 4#8 3 in 14 in
Please answer all question, it’s one question but was devised into 3 sections. Thanks! 5. For a reinforced concrete beam,if the reinforcing steel has a yield strength of so si andthe whatis the modular ratio? the re of 50 ksi and the 6. For the reinforced concrete beam shown below, what is the stress in the concrete and in the ular (10 pts) ght concrete has Ec reinforcing steel for the given bending moment and material properties using the rectang...
Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-way slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly distributed, factored load of 5 k/ft. (b) Design the slab reinforcement for the positive moment region using a factored load of 500 psf....
Problem 1 (27 points) Consider composite beam shown in image below. a) Draw internal force diagrams (6) b) Draw transform section and find its moment of inertia (9) c) Draw normal stress and strain diagram at cross-section with max moment (6) d) Find shear stress at the interface between PVC and Escon (6) 500 lb 500 lb PVC Epvc 450 ksi Escon EF160 ksi 3 ft 3 ft in. 2 in 3 in. Problem 1 (27 points) Consider composite beam...
For the beam shown use f-3000 psi and fy 60000 psi. 1- Compute the effective flange width 2- Compute фМ, for the positive and negative moment regions and check ACI requirements for both sections. At the support, the bottom bars are in one layer and at mid-span, the # 8 bars are in the bottom layer and the # 7 bars are in a second layer. Assume 2.5 in concrete cover (from outside face of concrete to the center of...
(40 pts) The simply supported beam shown in the figure below is being designed for shear. #3 stirrups (Grade 40) are to be used. 2. Wu = 4 kips/ft (includes self weight) wDL-1 kips/ft, wu 1.75 kips/ft h= 18" d = 15" L=20ft- fe-4000 psi Yoon- 150 lbf/t E-29,000 ksi fy60 ksi 2 IS Draw the factored shear envelope for Vu c. d. Determine the resistance to shear provided by the concrete. Are there any regions where no shear stirrups...
4. For the beam shown below,fe' = 4000 psi and fy = 60,000 psi. (20 points) (a) Compute the effective flange width at midspan. 911-6 in (a) Beam section and distance to adjacent beams Support (negative bending) Midspan positive bending) 7 No. 7 bars IIT 3 No. 8 plus 2 No. 7 bars at midspan 22 2 No. 8 bars at ends (b) Beam span supported by 18-in. wide columns (b) Compute Mn for the positive and negative-moment regions and...
b.323 The empirical provisions of 6.3.2.1 and 6.3.2.2 were developed for nonprestressed T-beams. The flange widths in 6.3.2.1 and 6.3.22 should be uset Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-wav slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly...