Question

Problem 2 (30 pts): Consider a two-stage vapor-compression refrigeration system operating between the pressure limits of 1.5

please answer all parts and show all work. Please include P-h chart work as welll



01992 American Society of Heating Refrigerating and Air Conditioning Engineers, Ine. Sea Level 10 110 333333 APPENDIX by Copl
0 0
Add a comment Improve this question Transcribed image text
Answer #1

A two-stage cascade refrigeration system is considered. Each stage operates on the ideal vapor-compression cycle with refrigerant-134a as the working fluid. The mass flow rate of refrigerant through the lower cycle, the rate of heat removal from the refrigerated space, the power input to the compressor, and the COP of this cascade refrigerator are to be determined.

Assumptions

1 Steady operating conditions exist.

2 Kinetic and potential energy changes are negligible.

3 The flash chamber is adiabatic.

QH Condenser 5 Expansion valve High-press. Compressor 4 6 9 Flash chamber 3 2 Expansion valve Low-press. Compressor LE 8 EvapTA 1.5 MPa 0.45 MPa A 0.15 MPa 6 39 B 8 9.

Analysis

(a) The properties are to be obtained from the refrigerant tables (Tables A-11 through A-13 of Yunus Cengel Textbook of Thermodynamics):

using R134a pah chart 1 Table hi hg @ 0.15 mpa 240.14 kJ/kg Si = Sg @ 0:15. MPa = 0.9 4.323. KI/kg. ha 262.7 KJ/kg @ P2=0.45

Add a comment
Know the answer?
Add Answer to:
please answer all parts and show all work. Please include P-h chart work as welll Problem...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem 2 (30 pts): Consider a two-stage vapor-compression refrigeration system operating between the pressure limits of...

    Problem 2 (30 pts): Consider a two-stage vapor-compression refrigeration system operating between the pressure limits of 1.5 MPa and 150 kPa with refrigerant-134a as the working fluid. The refrigerant leaves the condenser as a saturated liquid and is throttled to a flash chamber operating at 0.45 MPa. The mass flow rate of the refrigerant through the low pressure compressor is 0.15 kg/s. Assuming the refrigerant leaves the evaporator as a saturated vapor, determine (a) the mass flow rate of the...

  • A two-stage cascade refrigeration system operates between the pressure limits of 1.4MPa and 200 kPa with...

    A two-stage cascade refrigeration system operates between the pressure limits of 1.4MPa and 200 kPa with refrigerant-134a. The fluid leaves the condenser as a saturated liquid and is throttled to a flash chamber operating at 0.50 MPa. Part of the refrigerant evaporates in the flashing process, and this vapor is mixed with the refrigerant leaving the low-pressurin compressor. The liguid in the flash chamber iS throttled to the evaporator pressure and cools the refrigerated space. The mass flow rate of...

  • -Week 12 6 Help S Required information NOTE: This is a multi-part question. Once an answer is sub...

    -Week 12 6 Help S Required information NOTE: This is a multi-part question. Once an answer is submitted. you wiw be unable to retuwn to this part A two-stage compression refrigeration system operates with refrigerant-134a between the pressure limits of 1.4 MPa and 010 MPa. The refrigerant leaves the condenser as a saturated liquid and is throttled to a flash chamber operating at 0.6 MPa. he flash chamber is maintained at the same pressure as the low pressure discharge which...

  • A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0 and 0.1 MPa. Th...

    A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0 and 0.1 MPa. The refrigerant leaves the condenser as saturated liquid and is throttled to a flash chamber operating at 0.5 MPa. The refrigerant leaving the low-pressure compressor at 0.5 MPa is also routed to the flash chamber. The vapor in the flash chamber is then compressed to the condenser pressure by the high-pressure compressor, and the liquidis throttled to the evaporator pressure. Assume...

  • The coefficient of performance-of vapor-compression refrigeration cycles

    a) The coefficient of performance-of vapor-compression refrigeration cycles improves when the refrigerant is subcooled before it enters the throttling valve Can the refrigerant be subcooled indefinitely to maximize this effect, or is there a lower limit? Explain brieflyb) A two-stage compression refrigeration system with a flash chamber is used to produce chilled water for a commercial building The refrigeration system operates between a pressure limits of 1 2 MPa and 200 kPa with refrigerant-134a as the working fluid. The refrigerant leaves...

  • NOTE: This is a multi-part question Once an answer is submitted you will be unable to return to t...

    NOTE: This is a multi-part question Once an answer is submitted you will be unable to return to this part Consider a two-stage cascade refrigeration system operating between the pressure limits of 1.4 MPa and 140 kPa with refrigerant-134a as the working fluid. Heat rejection from the lower cycle to the upper cycle takes place in an adiabatic counterflow heat exchanger where the pressure in the upper and lower cycles are 0.7 and 08 MPa, respectively. In both cycles, the...

  • 1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated...

    1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 16 °C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and -34°C and the compressor is estimated to gain a net heat of...

  • Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124...

    Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124 kg/s, and it leaves at 0.7 MPa and 50°C. The refrigerant is cooled in the condenser to 24°C and 0.65 MPa, and it is throttled to 0.15 MPa. Disregarding any heat transfer and pressure drops in the connecting lines between the components, determine (a) the rate of heat removal from the refrigerated space and the power input to the compressor...

  • A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at by The refrigerant enters the condenser at compressor consumes 3.3 kW of power, dete...

    A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at by The refrigerant enters the condenser at compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b) the refrigeration load, (e) the COP, and (d) the g waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. 1.2 MPa and 50°C and leaves at the same...

  • 1. Refrigerant 134a enters the compressor of a refrigerator as superheated vapor at 0.20 MPa and...

    1. Refrigerant 134a enters the compressor of a refrigerator as superheated vapor at 0.20 MPa and -10 °C at a rate of 0.07 kg/s, and it leaves at 1.2 MPa and 70 °C. The refrigerant is cooled in the condenser to 44 °C and 1.130 MPa and it is throttled to 0.20 MPa. Disregarding heat transfer and pressure drop in the connecting lines between the components, show the cycle on a T-s diagram with respect to the saturation line. Determine...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT