3) Consider the below 3 phase network. There are distributed loads at only ACB and ADB...
3) Consider the below 3 phase network. There are distributed loads at only ACB and ADB branches. The ACB branch has )=50W/m and ADB branch has J-30 W/m. Allowable maximum voltage reduction is 6%. Rated voltage of the system is 380V. Please find the cable cross-section for both ACB and ADB branches. (Cables are copper and underground. = 56 m/2mm) Please note that there is not any voltage reduction at TA and TB lines which means you will not consider these lines 200m 600m C 400m 15kW 15kw B 500m D 300m 40kW