Question

equivalent resistance of 3 percent and a reactance of 9 percent per unit. (a) What is the transformers phase impedance refer

A 50-kVA, 13,800/208-V, Delta to Wye connected distribution transformer has an equivalent resistance of 3 percent and a reactance of 9 percent per unit.
(a) what's the transformers phase impedance referred to the high side voltage?
(b) what's the transformers voltage regulation at full load and 0.9 PF leading?

0 0
Add a comment Improve this question Transcribed image text
Answer #1

50. KVA o-Y 138001208 - V Arpu = 3% %dp.ung ay 3 r = 0.03 x 50X10 こ 0.03 13800 SOXIO3 3x 13800 3 x 138002 50KVA 1380 8800/2 2

Add a comment
Know the answer?
Add Answer to:
A 50-kVA, 13,800/208-V, Delta to Wye connected distribution transformer has an equivalent resistance of 3 percent...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 4. [Transformer - 15 points) A 50-kVA, 13,800/208-V, A-Y distribution transformer has an equivalent resistance of...

    4. [Transformer - 15 points) A 50-kVA, 13,800/208-V, A-Y distribution transformer has an equivalent resistance of 3 percent and a reactance of 9 percent per unit. (a) What is the transformer's phase impedance referred to the high-voltage side? (b) Calculate this transformer's voltage regulation at full load and 0.9 PF leading.

  • A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20...

    A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load 120 KVA, 90KW (lagging power factor) at rated terminal voltage of 208V Determine a) b) c) The approximate equivalent circuit referred to the low-voltage side The primary voltage The transformer efficiency Please show the following: Circuit with the values given & found Equations used A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load...

  • Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp...

    Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp 322 X,-45 Ω R,-0.05 Ω X,-0.06 Ω The excitation branch impedances are given referred to the high-voltage side of the transformer. (a) Find the equivalent circuit of this transformer referred to the high-voltage side. (b) Assume that this transformer is supplying rated load (20kVA) at 480 V and 0.8 PF lagging. What is this transformer's input voltage? What is its voltage regulation? (c) What is the transformer's...

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...

  • Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of thr...

    please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...

  • The equivalent resistance and equivalent reactance (high side) for a 35.8-kVA, 5800--900-V,50-Hz transformer are 2.5 Ohms...

    The equivalent resistance and equivalent reactance (high side) for a 35.8-kVA, 5800--900-V,50-Hz transformer are 2.5 Ohms and 6.4 Ohms, respectively. If a load impedance of 12 cis 16 Ohms is connected to the low side, determine the voltage across the load.

  • 3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase...

    3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...

  • A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit...

    A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit reactance of 5%. The open-circuit test performed on the low voltage side of the transfromer yielded the following data: VOC=13.8 kV, IOC=21.1 A, and POC=90.8 kW. (a) Find the equivalent circuit referred to the high voltage side of this transformer. (b) If the transformer is operating at full-load and at 0.8 pf lagging, find the voltage regulation of the transformer at this operating condition.

  • 1. A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has...

    A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 Wper phase. It is operated in parallel with a three-phase, 208 V, 60 Hz power supply.Determine the excitation voltage and the power angle when the machine is delivering rated kVA at 0.8 pf lagging. Draw the phasor diagram

  • 3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2...

    3.) The equivalent low-side parameters of a 250-KVA, 4160480-V, 60 Hz transformer are Reals 0.00920 2 and Xeais 0.0433 12. The transformer is operating in the step-down mode and is delivering rated current at rated voltage to a 0.840 power-factor lagging load. Determine (a) the no- load voltage; (b) the actual input voltage at the high side; (c) the high-side current; (d) the input impedance; (e) the voltage regulation; the voltage regulation if the power factor of the load is...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT