Question

A small factory has different types of loads which are grouped together as follows

A) induction motors : 1200 hp, 0.8 lag PF

B) Heating loads: 100kW at unity PF

A 3 phase synchronous motor is installed at the factory to improve the factory's overall power factor. Calculate how much reactively power per phase the synchronous motor must supply to the system to maintain an overall power factor of 0.9 lagging. 1 hp = 0.746 kW

together as follows: a. Induction motors: 1200 hp, 0.8 lagging power factor; b. Heating loads: 100 kW at unity power factor.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Hey there! Hope the solution is clear. Thank you and all the very best :)е, а Top Heating Lea lea I m m For induction motor, Active power absorbed, P₂ = 1200 СР 1200 » 0.74 6 895.2 KW. Pf cos Oz - 0Reactive power taken, For the synchronous motor, sogno Let the reactive power supplied by the motor be Qc and it is calso ass

Add a comment
Know the answer?
Add Answer to:
A small factory has different types of loads which are grouped together as follows A) induction...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three-phase induction motor delivers 500 hp at an efficiency of 0.91, the operating power factor...

    A three-phase induction motor delivers 500 hp at an efficiency of 0.91, the operating power factor being 0.76 lagging. A loaded synchronous motor with a power consumption of 100 kW is connected in parallel with the induction motor. Calculate the necessary kVA and the operating power factor of the synchronous motor if the overall power factor is to be unity. Answer should be 365 kVA, 0.274

  • 1. (10 points total) A source supplies power to the following three loads connected in parallel:...

    1. (10 points total) A source supplies power to the following three loads connected in parallel: (1) a lighting load drawing 10 kW, (2) an induction motor drawing 10 kVA at 0.90 power factor lagging, and (3) a synchronous motor operating at 10 hp, 85% efficiency and 0.95 power factor leading (1 hp 0.746 kW). (a) Determine the real, reactive, and apparent power delivered by the source. (8 points)

  • Three loads are being supplied from an infinite bus operating at 400 V. Load 1 is...

    Three loads are being supplied from an infinite bus operating at 400 V. Load 1 is an induction motor consuming 50 kW at 0.7 PF lagging, Load 2 is an induction motor consuming 200 kW at 0.85 PF lagging. Load 3 is a synchronous motor whose real power consumption is 100 kW. If Load 3 is adjusted to operate at 0.8 PF leading, what is total current drawn from infinite bus by the loads?

  • 1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF...

    1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...

  • (a) A 240 V 50 Hz factory electrical system has the following loads connected in parallel:...

    (a) A 240 V 50 Hz factory electrical system has the following loads connected in parallel: Load 1: 4 kW at a power factor of 0.8 lag Load 2: 6 kVA at a power factor of 0.6 lag Load3: 6.5 kVA with 2.5 kVAr of leading reactive power Determine: (C) the overall system power factor, (ii) the value of a power-factor correction capacitor to improve the power factor to unity, and (ii) the value of a power-factor correction capacitor to...

  • 2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a...

    2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a synchronous reactance of 0.6 and negligible armature resistance. Ignore the mechanical and core losses. The magnitude of the internal machine voltage is 480 V when the field current is 4 A. Assume magnetic linearity. Initially, the motor operates at the rated conditions. a) Find the speed of this motor. b) Find the armature and field currents. c) What is the developed torque? What is...

  • 3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power...

    3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.

  • Problem 3:A 480 V, 50 kW, 60 Hz, 3-φ synchronous motor has a synchronous reactance of Xs = 4.56 Ω and an armature-to-field mutual inductance, Laf = 150 mH. The motor is operating at rated speed an...

    Problem 3:A 480 V, 50 kW, 60 Hz, 3-φ synchronous motor has a synchronous reactance of Xs = 4.56 Ω and an armature-to-field mutual inductance, Laf = 150 mH. The motor is operating at rated speed and terminal voltage and at an output power of 35kW. Neglecting losses in the motor, calculate the magnitude and phase angle of the line-to-neutral generated voltage Eaf and field current I if the motor is operating at (a) 0.9 power factor lagging (b) unity...

  • Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a...

    Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...

  • THESE ARE QUESTION FROM THE TOPIC POWER FACTOR IMPROVEMENT FROM THE SUBJECT POWER SYSTEM FUNDAMENTALS PLEASE...

    THESE ARE QUESTION FROM THE TOPIC POWER FACTOR IMPROVEMENT FROM THE SUBJECT POWER SYSTEM FUNDAMENTALS PLEASE DO THE QUESTIONS STEP BY STEP AND IN NEAT HAND WRITTING THE ANSWERS ARE GIVEN WITH THE QUESTIONS 1) . A 3-phase, 400 V synchronous motor having a power consumption of 50 kW is connected in parallel with an induction motor which takes 200 kW at a power factor of 0·8 lagging.    (i) Calculate the current drawn from the mains when the power...