A )
In simple terms Wet bulb temperature tells you how easy it is for water to evaporate
If you consider air which can be cooled by evaporation
Upto - 100% relative humidity , (that is you can't add any more
water in it )
then "The colling effect that occurs by adiabatic evaporation of
water is called
WB temp"
WB thermometer measure the latent heat of a moisture loaded air
Humans sweat by means of evaporation normally, when you want to know how well water will evaporate, you need to know the difference between the wet bulb and dry bulb temperatures , if the difference is 0 there will be no evaporation and no heat transfer could occur between skin and ambient.
B ) Psychrometric Chart of Process :
iv ) Standart Relative relative humidty range is 30% - 50%
as in this process after heating it is less than 20%.
so it is not acceptable to supply in room.
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. (Note that air...
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...
- What is the physical interpretation of the wet-bulb temperature During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 min of room return air at 30°C. SON relative humidity is first mixed with 40 m/min of outdoor at 10°C. 20% relative humidity: The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. Note that air and...
al What is the physical interpretation of the wet-bulb temperature! b] During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C. 50% relative humidity is first mixed with 20 m/min of outdoor 10°C. 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air and...
Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note...
Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note...
a) what is the physical interpretation of the wet-bulb temperature? b) during winter time a room is maintained at a steady temperature and humidity by an air-conditionibg system shown. 200 m^3/ min of room return air at 30 c, 50% relative hunidity is first mixed with 40 m^3/min of outdoor at 10 c, 20% relative humidity. the mixed air is then introduced to a heater where the temp of air is raised to 45 c and supplied to the room....
Question 2 aj What is the physical interpretation of the wet-bulb temperature? bi During winter time aroom is maintained at a steady temperature and humidity by an air-conditioning system shown 200 mimin of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. Note that...