Question

a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady te

0 0
Add a comment Improve this question Transcribed image text
Answer #1

SUBPART A

When a thermometer is used to take the reading of the atmospheric air, but its bulb is covered in a wet cloth with air flowing over it, then the temperature recorded is the WBT of the room air. Now the important thing to note is that air can only absorb a certain amount of moisture in itself. When the moisture from the wet-bulb/cloth is converting into vapour, then it takes place by absorbing some heat from the bulb, thus lowering its temperature. Hence the WBT is always lesser than the DBT or normal temperature. Now as the relative humidity increases, the ability to absorb of the room air to absorb the moisture decreases. When it gets completely saturated, the moisture on the bulb does not vaporize. Hence it does not absorb any heat from the bulb, and thus the WBT becomes same as the DBT. Hence the significance of WBT is that it gives us an idea about the moisture content in the atmosphere. Closer the WBT to the actual temperature, higher is the moisture content of the atmosphere

SUBPART B

Important assumptions are

  • Mixing is adiabatic in nature
  • The heater is 100% efficient.

part 1

The process as depicted on a psychrometric chart is as follows:- (Please note that due to copyright issues I am not allowed to use ASHRAE psychrometric chart)

Specific volume (m®/kg) Relative humidity (%) 100 90 80 180/ 70 Absolute humidity (kg/kg) 60 50 40 -0.0550 170) 30 -0.0500 16

part 2

From the chart, we aquire the following data which we will need in our calculations

  • Volume flow rate at 'mix' V = 200+40 = 240 m3/min = 4 m3/s
  • density at 'mix' rho = 1.17 kg/m3
  • specific enthalpy at 'mix' h1 = 55.2 kJ/kg
  • specific enthalpy at 'exit' h2 = 74.2 kJ/kg

Thus the capacity of the steam heater needs to be Q = V*rho*(h2-h1) = 4 * 1.17 * (74.2-55.2) = 88.92 kW

part 3

From the chart, we see that the exit relative humidity is at 18.7%

part 4

Frankly speaking, only a vague answer can be presented to the asked question. This is because "common engineering practices" can vary over a wide range, whose requirements vary accordingly. Our output air has high temperature and low relative humidity. This means that evaporation of water is rapid, and there are little to no chances of problems caused by high moisture content occurring. Hence this is perfect for electronic devices, for which moisture is bad. On the other hand, high evaporation rates can cause heat to be extacted from materials fast enough to cause shrinkage. This can be bad for materials like metals and concretes as they may give rise to surface defects (similar to our lips cracking during winter).

part 5

At 150 kPa, the enthalpy of saturated vapour is hw1 = 2693.11 kJ/kg, and the enthalpy of saturated liquid is hw2 = 467.08 kJ/kg

Thus the required mass flow rate of steam is Q/(hw1-hw2) = 88.92/(2693.11 - 467.08) = 0.0399 kg/s


*A humble request* - If you have any doubt, please use the comment section to communicate. Please be a little patient, it is an honest promise I will reply as soon as possible. This will clarify your doubt, and also help me to get better at answering your next questions. At the same time, If my answer helped you, please consider leaving an upvote. I hope you understand my viewpoint. Thank you :)

Add a comment
Know the answer?
Add Answer to:
a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...

    a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...

  • - What is the physical interpretation of the wet-bulb temperature During winter time a room is...

    - What is the physical interpretation of the wet-bulb temperature During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 min of room return air at 30°C. SON relative humidity is first mixed with 40 m/min of outdoor at 10°C. 20% relative humidity: The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. Note that air and...

  • a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...

    a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 mº/min of room return air at 30°C, 50% relative humidity is first mixed with 40 mº/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. (Note that air...

  • a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...

    a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...

  • a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...

    a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...

  • Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time...

    Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note...

  • Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time...

    Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note...

  • al What is the physical interpretation of the wet-bulb temperature! b] During winter time a room...

    al What is the physical interpretation of the wet-bulb temperature! b] During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m/min of room return air at 30°C. 50% relative humidity is first mixed with 20 m/min of outdoor 10°C. 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air and...

  • a) what is the physical interpretation of the wet-bulb temperature? b) during winter time a room...

    a) what is the physical interpretation of the wet-bulb temperature? b) during winter time a room is maintained at a steady temperature and humidity by an air-conditionibg system shown. 200 m^3/ min of room return air at 30 c, 50% relative hunidity is first mixed with 40 m^3/min of outdoor at 10 c, 20% relative humidity. the mixed air is then introduced to a heater where the temp of air is raised to 45 c and supplied to the room....

  • Question z SU POLOHG a) What is the physical interpretation of the wet-bulb temperature? b) During...

    Question z SU POLOHG a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT