A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected l

0 0
Add a comment Improve this question Transcribed image text
Answer #1


Zline = (0.25 +j 1.25)~/ph. Load 1 Po = 125kw, Bi - 100 KVAR S, = {60.078/38-66°) kV4; 0,238.66* Londa o Land Za = (25+)40)up 3 Load, Silpha 160.078/28.66 ) xr03 silph = 53-359 kVA. silph Il v(ph) I, = 22.233A, Ī, - 11/01 Ij =(22.2331-38-66°)4- 53.359II,tiIz 22.2331-38-66*+54.8591-17.75+16:671-36-87 I 17-36-313-89+ 52-247-j16-125+ 13.336-j10 Ī =(22-3534-26.09) 4 A: Vs (ph)

Add a comment
Know the answer?
Add Answer to:
A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 5. The line to neutral voltages of a Y-connected three phase source are given by, The...

    5. The line to neutral voltages of a Y-connected three phase source are given by, The above three phase source is directly connected to a delta connected balanced three phase resistive load. The resistance in each phase is 10 ohms. Calculate the current phasor 0. Answer- 4. Following three loads are connected in parallel across a single-phase source voltage source: Load 1 absorbs 15 kW and 6.667 kvar; Load 2 absorbs 3 kVA at 0.96PF leading; Load 3 absorbs 15...

  • Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...

    Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400+j300 2/0; load 2 is A-connected with an impedance of 2400-j18000/0; and load 3 is 172.8+j2203.2 kVA. The loads are fed from a distribution line with an impedance of 2+j16 0/0. The magnitude of the line-to-neutral voltage at the load end of the line is 2413 kV. Calculate the total complex power at the sending end of the line. :) Magnitude of the total...

  • Problem 3: (20 points) ase serves two balanced parallel loads. The line- A three-phase transmission line...

    Problem 3: (20 points) ase serves two balanced parallel loads. The line- A three-phase transmission line with an impedance (0.2 +j1.0) 12/phase serves two balan to-line voltage at the load end of the line is 480 V (rms). Load 1: Wye-connected and absorbs a total of 200 kW with a lagging p.f. of 0.87. Load 2: Delta-connected with an impedance of (20+30) 2/phase. a. Draw the single phase representation of the circuit b. How much current flows through phase A...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • 1. Solve the following three-phase problem A 3-phase line has an impedance of 0.6+j3 Q/phase. The...

    1. Solve the following three-phase problem A 3-phase line has an impedance of 0.6+j3 Q/phase. The line feeds three balanced loads that are connected in parallel. The first oad is absorbing a total of 156kW+jl17kVar, the second load is A connected and has an impedance of 144-j42 Q/phase, and the third load is 115KVA at 0.6 lagging P.F. .The line to neutral voltage at the load end is 2400 volts. a. Find the line voltage at the source end b....

  • Please quickly .I will grade 2. Three balanced three-phase loads are connected in parallel. Load 1...

    Please quickly .I will grade 2. Three balanced three-phase loads are connected in parallel. Load 1 is Y- connected with an impedance of 400 + 13001/0 load 2 is A-connected with an impedance of 2400 - 218000/0; and load 3 is 172.8 + j2203.2 kVA. The loads are fed from a distribution line with an impedance of 2 + j1612/0. The magnitude of the line-to-neutral voltage at the load end of the line is 24V3 kv. a) Calculate the total...

  • 508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an...

    508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...

  • Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation...

    Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the...

  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two...

    A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two balanced three phase loads that are connected in parallel. The first load is absorbing 560.1kVA @ PF=0.707 lagging and the second load absorbs 132kW @ PF=1. The line-to-line voltage at the load side is 3810.5/_30° V. Determine: a) The magnitude of the line voltage at the source side b) Total active & reactive power loss in the line c) Active and reactive power at...