5. The line to neutral voltages of a Y-connected three phase source are given by, The...
A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...
A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 0.5-H inductance in series with a 50-Ω resistance. Assume that the phase of Van is zero. home / study / engineering / electrical engineering / electrical engineering questions and answers / A Balanced Positive-sequence Wye-connected 60-Hz Three-phase Source Has Line-to-line Voltages ... Question: A balanced positive-sequence wye-connected...
The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a line-to-line voltage of 480 V. The loads are described below: • Load 1: ∆-connected, total three-phase apparent power is 30 kVA at 0.95 power factor lagging. • Load 2: ∆-connected, total three-phase active power is 20 kW at 0.7 power factor lagging. • Load 3: Y-connected, phase current is 30 A, and power factor is 0.9 pf leading. (a) Calculate the total complex power...
P 5.103 A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 05-11 inductance in series with a 30Ω resistance. Assume that the phase of Van is zero. Part A Pl Find the line-to-neutral voltage phasor Van Enter your answer using polar notation. Express argument in degrees. 이미? Subrmit X Incorrect, Try Again; 5 attempts remaining Part B...
Please show how this transformers problem is done. Thanks!
Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a balanced three-phase load (it doesn't matter whether the load is Y or Delta connected). The voltage and current of the source are: van (t) - 340 sin (377t + 0.5236) ia(t) 100sin (377t 0.87266) Calculate the following: (a) The rms phase voltage (Van, magnitude and phase). (b) The rms line-to-line voltage (Vab, magnitude and phase) (c) The...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
A balanced three-phase source with a 208 V rms (line-to-line) is delivering power to a balanced Y-connected load with phase impedance Z1 = 4 + j 3 Ohms in parallel with a balanced delta-connected load with phase impedance Z2 = 7.5 + j 6 Ohms. Calculate the active (real) and reactive (imaginary) powers delivered by the source. Draw the power triangle. What is the power factor of the combined load?
10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...
of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is connected to the following loads via 0.5+0.25 j 0/phase line. A Y-connected 900 kVA at 0.7 pf lagging load. · A ?-connected 500 kw at 0.6 pf lagging load. A Y-connected 350 kVAR at 0.7 pf lagging load. · 4-connected 600 kW at 0.6 pf lagging load. A Part 1: If the load voltage is always kept at 11 kV a) what is the...