Question

of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is connected to the following loads via 0.5+0.25 j 0/phase line. A Y-connected 900 kVA at 0.7 pf lagging load. · A ?-connected 500 kw at 0.6 pf lagging load. A Y-connected 350 kVAR at 0.7 pf lagging load. · 4-connected 600 kW at 0.6 pf lagging load. A Part 1: If the load voltage is always kept at 11 kV a) what is the total complex power consumed by the total load? Stot b) Find the three phase line current supplying the total load.I c) Find the three phase supply phase voltages. Van,Vbn, Vcn (4%) SOLUTION a) What is the total complex power consumed by the total load? S
0 0
Add a comment Improve this question Transcribed image text
Answer #1

load1:

900*10^3=1.732*11*10^3*I1

I1=[900*10^3]/[1.732*11*10^3]=47.23<-inverse cosine of 0.7=47.23<-45.57 amps.

load 2:

500*10^3=1.732*11*10^3*I2*0.6

I2=[500*10^3]/[1.732*11*10^3*0.6]=43.73<-inverse cosine of 0.6=43.73<-53.13 amps.

load 3:

350*10^3= 1.732*11*10^3*I3*SINE(INVERSE COSINE OF 0.7)

I3=[350*10^3]/[1.732*11*10^3*0.714]=25.72<-INVERSE COSINE OF 0.7=25.72<-45.57 amps.

load 4:

600*10^3=1.732*11*10^3*I4*0.6

I4=[600*10^3]/[1.732*11*10^3*0.6]=52.48<-INVERSE COSINE OF 0.6=52.48<-53.13 amps.

b) total load current=I1+I2+I3+I4=168.79<-49.87 amps.

a) s=3*[11000/1.732]*168.79<-49.87=3215881.414<-49.87 VA

c)per phase load voltage=11000/1.732=6350.85 volts.

Van=6350.85<0+(0.5+j0.25)*168.79<-49.87=6437.616<-0.3322 volts

Vbn=6437.616<(-0.3322-120)=6437.616<-120.3322 volts.

Vcn=6437.616<(-0.3322+120)=6437.616<119.6678 volts.

Add a comment
Know the answer?
Add Answer to:
of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a...

    The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a line-to-line voltage of 480 V. The loads are described below: • Load 1: ∆-connected, total three-phase apparent power is 30 kVA at 0.95 power factor lagging. • Load 2: ∆-connected, total three-phase active power is 20 kW at 0.7 power factor lagging. • Load 3: Y-connected, phase current is 30 A, and power factor is 0.9 pf leading. (a) Calculate the total complex power...

  • A generator is supplying two loads at 2800V and 60 Hz. The loads are: Load 1:...

    A generator is supplying two loads at 2800V and 60 Hz. The loads are: Load 1: 10 kVA, at 0.6 pf lagging. Load 2: 12 kW and 10 KVAR inductive a. Calculate the total active and reactive power, and the power factor of the load. S- S, - ST- Pr- PF-

  • A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel...

    A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?

  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • Example 9 Three loads are connected in parallel across 1400 V, 60 Hz supply: Load 1:...

    Example 9 Three loads are connected in parallel across 1400 V, 60 Hz supply: Load 1: 125 KVA, 0.28 PF lag Load 2: 10 kW, 40 kVAR capacitive load Load 3: 15 kW Find the total kW, kVAR, KVA, and the supply power factor . The KVAR and the capacitance in mF of the capacitor needed to improve the PF to 0.8 lagging

  • 5. The line to neutral voltages of a Y-connected three phase source are given by, The...

    5. The line to neutral voltages of a Y-connected three phase source are given by, The above three phase source is directly connected to a delta connected balanced three phase resistive load. The resistance in each phase is 10 ohms. Calculate the current phasor 0. Answer- 4. Following three loads are connected in parallel across a single-phase source voltage source: Load 1 absorbs 15 kW and 6.667 kvar; Load 2 absorbs 3 kVA at 0.96PF leading; Load 3 absorbs 15...

  • Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...

    Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400+j300 2/0; load 2 is A-connected with an impedance of 2400-j18000/0; and load 3 is 172.8+j2203.2 kVA. The loads are fed from a distribution line with an impedance of 2+j16 0/0. The magnitude of the line-to-neutral voltage at the load end of the line is 2413 kV. Calculate the total complex power at the sending end of the line. :) Magnitude of the total...

  • 3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power...

    3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.

  • Problem 3 Two parallel 3-phase loads are supplied from a 3-phase source with line-line voltage of...

    Problem 3 Two parallel 3-phase loads are supplied from a 3-phase source with line-line voltage of 415.6922 V rms. The data of their power consumption are as follows. Load 1: 15 kVA at power factor of 0.75 lagging Load 2: 9 kW at power factor 0.82 lagging 1) 2) 3) 4) 5) Determine the complex power consumed by Load 1 Find the complex power consumed by Load 2 Calculate the total complex power consumed by the two loads. Determine the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT