Question

A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and 0-8 p.f. lagging. The total resistance 25.3 ohm
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Sol& Given that x. Receiving end voltage & r = 124 kv * Receiving end power Py = 60 MVA + 0.8 (34) = 48 MWI 1: power factor cHere da propagation constant 2. Vzy 7e = characteristic impedance of the line 7 = Series impedance / km 3=8r+ful eelkm = shun* propagation constant d-day = 10.0843+30.2217) (91-473-*17* = 0.0001 +$0.0006 = 0.0006 L79.5905 *. 8l=8*300 = 0.0320 +j 0:171.0325199923° = 0.१685 -१.११२३ 8) -1 x. Cosb e+e (1.0325 L१.११ 23) +(०.१685 - १.११23 ) = 0.9853 + 500055 = 0.१853 103228 * si4. c sinh81 - (no). 276 2 I-lo-40% 4) ( 0-17 4 7. 7/) - 25.024.5 +966-2311 = 70.8011 L69.3015 0.1764 279.7109 sinhal Zc 401.*. Pr = 3 1 Vorph) | Irph I cosør Pr . (IrphI= 2 Vyph) coser = 48+10% 38 124*1870.8 VB T = 279.3630 Amp i Irph = | Irphl Edo* Sending end current Isph = (Voph +D Ir ph = (4.3959 *rā9 L90./203°) (71.5914 *1ồ LO ) +(0.9853 L0.3228°) ( 279.3630 L-36.86(LLC) input power Ps= 3/vsph) |Isph) cosas Ps = 3* 87.923 #1ồ * 257.7023 * 0.7867 Ps = 53.475MWI output & Transmission efficiNOTE We can solve this problem by using approximate ABCD parameters of tong transmission line L 131121 A=D= 1+ 21 B= 2 (1+ 2

Add a comment
Know the answer?
Add Answer to:
A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f...

    A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f lagging and at 110 kV. The resistance and reactance per phase per km are (0.2) Ω and (j0.4) Ω respectively, while capacitive admittance per phase per km is (j2.5 * 10-6) siemen. Using nominal T circuit, Find: 1- Constants A, B, C, and D. 2- Sending end voltage.        3- Sending end current 4- Sending end power factor    5- Voltage regulation of this T.L.    6-...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1 * 10^-6 s/km. Calculate the ABCD constants of this transmission line. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11. What is the efficiency of the...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 ohm/km, x = 0.88 ohm/km, y = 4.1 * 10^-6 S/km. 10. Calculate the ABCD constants of this transmission line. 11. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? 12. What is the voltage regulation of the transmission line for the conditions in question 11. 13. What is...

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1*10^-6 S/km. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11.

  • power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long....

    power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...

  • Problem 2: A 345 kV, 60 Hz, three-phase characteristic parameters of the transmission line are: transmission...

    Problem 2: A 345 kV, 60 Hz, three-phase characteristic parameters of the transmission line are: transmission line is 130 km long. The r= 0.036 ?/km L = 0.8 x 10-3 H/km C = 0.0112 x 10-6 F/km The receiving end load is 270 MVA with 0.8 PF lagging at 325 kV. (k) What is the total series impedance of this transmission line? (5 points) () What is the total shunt admittance of this transmission line? (5 points) (m) Calculate the...

  • A 220-kv, 150 MVA, 60-Hz three phase transmission line is 50 km long. The characteristic parameters...

    A 220-kv, 150 MVA, 60-Hz three phase transmission line is 50 km long. The characteristic parameters of the transmission line are r-0.05 2/km x-0.88 /km 1. The voltag at the reeioransmisson line is215 kV What is the suppling end voltage if the line is supplying rated voltage at unity PF? What is the voltage regulation of the transmission line? What is the efficiency of the transmission line? a. b. c.

  • QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per...

    QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per phase series impedance of 0,120 + 10,4325 per km. Detemine the sending end voltage, voltage regulation, the sending end power, and the transmission efficiency when the line delivers (a) 60 MVA, 0.8 lagging power factor at 60 kV. (b) 110 MW, unity power factor at 60 kV

  • A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2...

    A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...