On a cold winter day where the outside temperature is -10o C, a heat pump provides 20 kW to heat a house to 20o C. The heat pump has a COPHP of 4 at the maximum power. The next day a storm brings the outside temperature down to −15o C. If the ratio of COPHP and the reversible COPrev for day 1 and day 2 is the same, COPHP for both days is the same, and that the house loses heat to the outside air, extrapolate the temperature of the house on the second day. (Hint: use ratio of COPHP and COPHP,rev for both days).
Calculation for finding out temperature of the house on the second day is done below.
Note:
On a cold winter day where the outside temperature is -10o C, a heat pump provides...
A house uses a heat pump to maintain the indoor temperature at 22 C on a cold winter day when the outside temperature is -10 C. On this day, the house receives heat from the heat pump at a rate of 24 kW. Is it possible for this heat pump to operate at 2.5 kW? Justify your answer.
On a cold winter day, the outside temperature is -20°C and the inside temperature is maintained at 20°C. There is a net heat flow to the outside through the walls, roof, etc., of 25 kW. What is the rate of increase of the entropy of the universe as a result of this heat flow?
Problem 3 A home in a Midwestern city is being heated with a heat pump in a winter day where the outside temperature is 5 C. Due to poor insulation, the home loses 800 KW of heat to the outside surroundings. An space heater inside the room generates 150 KW and another 120 KW of heat is generated by all the appliances and people in the room. The home is desired to be maintained at 25°C The heat pump consumes...
A heat pump is to be used to heat a house in winter and then reversed to cool the house in summer. The interior space is to be maintained at 20oC. Heat transfer through walls and roof is estimated to be χ = 0.525 kJ/sec per degree difference in temperature between inside and outside. (6a) (8p) In winter if the outside temperature is 5oC, what is the minimum power required to drive the heat pump? (6b) (12p) For the same...
We propose to heat a house in the winter with a heat pump. The house is to be maintained at 20°C at all times. When the ambient temperature outside drops to -10°C, the rate at which heat is lost from the house is estimated to be 25 kW. What is the minimum electrical power (in kW) required to drive the heat pump? Use the correct sign convention to indicate the direction of work. Hint: the minimum power happens with the...
Anyone can help me with this question? 2 - Heat pump .The heat pump illustrated beside uses 1.5 kw mechanical power (that's is 1500 J/s) and extracts 1.2 million calories per hour from the outside air . A) How much heat is pumped into the house every day? .B) If this heat pump is made such that it is ideal and reversible, and you decide to heat your house with a gas furnace and use the heat pump as an...
On a cold winter day, the outside temperature is –5.0 °C while the interior of a well-insulated garage is maintained at 20.0 °C by an electric heater. Assume the walls have a total area of 75 m2, a thickness of 0.15 m, and a thermal conductivity of 0.042 W/(m · C°). What is the cost to heat the garage for six hours at these temperatures if the cost of electricity is $ 0.11/kWh? Note: 1 kWh = 3.6 × 106...
On a cold day, 26100 J of heat leaks out of a house. The inside temperature is 22 °C, and the outside temperature is -20 °C. What is the increase in the entropy of the universe that this heat loss produces?
The heat pump illustrated beside uses 1.5 kW mechanical power (that's is 1500 J/s) and extracts 1.2 million calories per hour from the outside air. • A) How much heat is pumped into the house every day? • B) If this heat pump is made such that it is ideal and reversible, and you decide to heat your house with a gas furnace and use the heat pump as an heat engine to produce mechanical work, then what would be...