Question
Please complete both, very confused
14. A device that establishes an electrical connection to the earth is a a grounding conductor C. grounding electrode b. equi
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Answer 14 ) option (a) is correct

Grounding conductor- grounding conductor is  used to connect electric equipment or the grounded circuit of an electric wiring system to a grounding electrode or electrodes.

Grounding Electrodes- A conductor buried in the ground, used to maintain conductors connected to it at ground potential and dissipate current conducted to it into the earth.

Equipment Grounding Conductor- The conductor used to connect the non-current-carrying metal parts of equipment, raceways and other enclosures to the system grounded conductor, grounding electrode conductor, or both.

Grounding Electrode conductor-The conductor used to connect the grounding electrode(s) to the equipment grounding conductor, to the grounded conductor, or to both, at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s).

Answer 15)option (a) is correct

The size of the equipment grounding conductor is based upon the rating or setting of automatic over current protective device in the circuit ahead of the electrical appliance or equipment.

Neutral is used by current for return path.

Phase is the main path of current supplied to equipment.

Add a comment
Know the answer?
Add Answer to:
Please complete both, very confused 14. A device that establishes an electrical connection to the earth...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Given: 100kVA single phase transformer, Z=1.5% Primary: 480V 2 wire Secondary: 120/240V 3 wire Install the...

    Given: 100kVA single phase transformer, Z=1.5% Primary: 480V 2 wire Secondary: 120/240V 3 wire Install the above transformer to serve a branch circuit panelboard. The panelboard will be located 10' from the transformer. The primary side raceway is PVC and the secondary raceway is EMT. All calculations will conform to applicable NEC regulations. The primary side, overcurrent protection device, will be chosen based on the next available standard size of the full load amps of the transformer. The secondary side,...

  • A) select the appropriate overcurrent protection device size, B) conductor size(s) (including equipment grounding conductor), C)...

    A) select the appropriate overcurrent protection device size, B) conductor size(s) (including equipment grounding conductor), C) conduit size(s) D) Draw a schematic representation of the circuit (conduit and tick marks) Please dont skip steps and label which tables you used! thanks 240V-іф branch circuit to an electric range with a continuous load of 8700 VA. Copper conductors, TW insulation, and ENT conduit. Use Chapter 9, Tables 4 and 5 for sizing the conduit. 4,

  • 1. The color of the outer finish of the insulation or tape marking a grounded conductor...

    1. The color of the outer finish of the insulation or tape marking a grounded conductor must be A. black B. green. C. white or gray D. yellow finish. 2. When the main bonding jumper in a residential el ectrical system is a screw only, the screw must be identified with a A. white B. red C. green D. black The grounding electrode conductor should be installed without a splice, unless the splice is made using exothermic welding or by...

  • 11. An electrical system that's not grounded and is between 120 and 1000 volts must include...

    11. An electrical system that's not grounded and is between 120 and 1000 volts must include the use of A. ground isolators. OB. equipotential barriers. C. ground detectors. OD. arc suppression. 12. Imagine that you're installing a feeder in a hospital that will terminate in five branch circuits in patient care areas. To make the feeder legal for this purpose in this area, you must O A. run two wire conductor EGCS. OB. use enhanced bonding practices on the feeder's...

  • 2- The Electrical System Unit 14 14.5 Premises Ground-Fault Current Path 14.8 Conductor Power Los Metal...

    2- The Electrical System Unit 14 14.5 Premises Ground-Fault Current Path 14.8 Conductor Power Los Metal parts of premises wiring must be bonded to a low medance path designed so that the circuit protection device will quickly open and clear a ground fault 12 Conductor poner losses are directly proporional tl le lengh of the conaco and the areofthe cnrt duce the line- aused by the current is doubled, the power loss will be increased by a) True -percent al...

  • pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC...

    pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...

  • UNIT 14 Practice Questions 4,5 Pr The multipoint grounded neutral is intended to reduce he PRACTICE...

    UNIT 14 Practice Questions 4,5 Pr The multipoint grounded neutral is intended to reduce he PRACTICE QUESTIONS 14.1 Current Flow 1. Electrons leaving a power supply are always trying to neutral voltage drop, assist in clearing to-neutral faults, and reduce elevated voltage causet line-to-ground faults return to the same power supply; they are not trying to g0 into the earth. (a) primary/primary (b) secondary/secondary (c) primary/secondary d) secondary/primary (a) True b) False 2 When alternating current is appled to the...

  • Electrical Knowledge: 1. Know what a multimeter is and how to use it. 2. Know how to field check a 3-phase AC motor for...

    Electrical Knowledge: 1. Know what a multimeter is and how to use it. 2. Know how to field check a 3-phase AC motor for proper operations. 3. Know grounds and shorts, and the proper way to test for them. 4. Be able to calculate current if given the number of volts and the amount of resistance in ohms. 5. Know about electrically operated control valves and how to troubleshoot if it will not actuate the valve. 6. Know the different...

  • 2.0 VI IRE You are to design the electrical system for a radiant heat system. The electrical supp...

    2.0 VI IRE You are to design the electrical system for a radiant heat system. The electrical supply will be to run the system The following information is the design information A single story building is shown in the attached drawing. .The electrical loads for the entire site is as follows: The building is to have 12,470VAC, 3-phase, 4-wire, 60Hz power supplied to the building transformers. The site requires the following loads: A motor distribution panel for 4 pumps each...

  • These questions are related to engineering codes and practices. Need help with these questions please. Have...

    These questions are related to engineering codes and practices. Need help with these questions please. Have to chose from the multiple choice options for each question below. Question 12 When testing the insulation resistance between the ground and the chassis, what result should you expect? A. The testing equipment will display a very low resistance at the end. B. The testing equipment will display a low voltage at the end. C. The testing equipment will display a high voltage at...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT