3) A two-winding transformer, three phase, 345/230 kV has a single phase capacity of 500 MVA:...
Question I The rating of a three phase three winding transformer are: Y-connected 10 KV 40 MVA Secondary Y-connected 22 KV 40 MVA A-connected 4 KV 15 MVA Primary Tertiary Neglecting winding resistance and exciting current, the per unit leakage reactance are: Mps 9.6 % pu on 40 MVA, 11022 KV xm = 7.2 % pu on 40 MVA, I 10/ 4 KV Xsti: 12 % pu on 40 MVA, 22/ 4 KV Determine the era nyimpedances of the transformer...
Problem 3. A three-phase transformer is constructed using three single-phase two-winding trans- formers, each has the same ratings of 500 MVA, 15/240 kV, and leakage impedance of XT.p.u 0.2 p.u The high-voltage side of the three-phase transformer is connected to a three-phase Y-connected load that absorbs 1000 MVA at 0.9 power factor (lagging). The phase-a voltage across the load is Van 2402(0) kV. Answer the following questions. [10 points] a) Calculate the phase-a voltage at the low-voltage side (denoted by...
The ratings of a three-phase, three-winding transformer are Y connected, 66 kV, 20 MVA Primary (1): Secondary (2):Y connected, 13.2 kV, 15 MVA Tertiary (3): A connected, 2.3 kV, 5 MVA Neglecting winding resistances and exciting current, the per-unit leakage reactances are: X12 0.08 on a 20-MVA, 66-kV base X13 0.10 on a 20-MVA, 66-kV base X23 0.09 on a 15-MVA, 13.2-kV base (a) Determine the per-unit reactances Xi, X2, X3 of the equivalent circuit on a 20- MVA, 66-kV...
1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown in Figure P1. Parameters of both generator and transformer are given in the figure. Transformer losses and exciting current are neglected. A three-phase short-circuit occurs on the line side of the circuit breaker when the generator is operated at rated terminal voltage and at no-load. The breaker interrupts the fault three cycles after fault inception. Neglect the effect of the transformer on the time...
_hint Ouestion 5: Three two-winding transformers are grounded Y-A connected to 230 kV on the Y-side and to 34.5 kV on the A-side. The combined three-phase rating of these transformers is 500 MVA. The per-unit reactance is 13% on the basis of the transformer rating. Calculate the rated values of voltage and currents, and Xps and Xsp (in ) in following figures Is Zpa.(M) + Пр n, (а) 1n Zap() V Пр п, (b) Q5: P 230 K 3u 5K...
A three-phase Y-A transformer is rated 225-kV:24-kV, 400 MVA and has a single-phase equivalent series reactance of 6.08 ? as referred to its high-voltage terminals. The transformer is supplying a load of 375 MVA at 0.89 power factor leading at a voltage of 24 kV (line to line) on its low-voltage side. It is supplied from a feeder whose impedance is 0.17 +/2.2 ? connected to its high-voltage terminals. For these conditions, calculate (a) the line-to-line voltage at the high-...
A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit reactance of 5%. The open-circuit test performed on the low voltage side of the transfromer yielded the following data: VOC=13.8 kV, IOC=21.1 A, and POC=90.8 kW. (a) Find the equivalent circuit referred to the high voltage side of this transformer. (b) If the transformer is operating at full-load and at 0.8 pf lagging, find the voltage regulation of the transformer at this operating condition.
Solution of two part please with steps Question 1: Ve-le The rating of s three phase three winding transformer are: Y-connected un KV 40 MVA Y-connected 22 KV 40 MVA 4 KV 15 MVA Primary Secondary Tertiary A-connected Neglecting winding resistance and exciting current, the per unit leakage reactance are X 9.6 % pu on 40 MVA. 110/22 KV X7.2 % pu on 40 MVA, 110/ 4 KV Xg 12 % pu on 40 MVA, 22 4 KV a) Determine...
A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...
Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA at 0.8 p.f. lagging Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA...