A system consists of two plants connected by a transmission line and a load that is located at plant 2. Data for the loss equation consists of the information that 100 MW transmitted from plant 1 to the load results in a loss of 10 MW and
where B11 is the only non-zero loss coefficient. Assume that the
incremental fuelcosts can be approximated by the following
equations:
Find the required generation for each plant and the power received by the load when ? for the system is $6 per Mwh.
A system consists of two plants connected by a transmission line and a load that is...
A transmission line consists of two parts, the first part has a rating of 0.15 dB / m with a length of 20 m. The second part has a length of 10 m with a rating of 0.959 dB / m and an impedance of 50 ohms. The reflected coefficient on the transmission line connection between the two parts is 0.3. The end of the second channel is connected with a load of 100 + j100 ohms. If the power...
Problem 2 The fuel-cost function in $/h of two thermal plants are ?1 = 320 + 6.2?1 + 0.004?1 2 , ?2 = 200 + 6.0?2 + 0.003?2 2 , where ?1 and ?2 are in MW. Plant outputs are subject to the following limits (in MW) Problem 2 The fuel-cost function in $/h of two thermal plants are C1 = 320 +6.2P2 +0.004P], C2 = 200 +6.0P2 + 0.003P2, where P and P2 are in MW. Plant outputs are...
A balanced A-connected load of Z,=12+39.0 12 is connected to a power supply via a transmission line with impedance of Zrl=0.6+j2.5 12, find Transmission Lines o 20820 V AC 2084(0–240°) v umaza 10 AC 2084(0-120°) v mm | za | Three-Phase 208 V, 60 HZ Power Supply Three-Phase A-Connected Balanced Load @@OGO E the load line and phase voltages (magnitude and angle), the load line and phase currents (magnitude and angle), the total load's real, reactive, and apparent powers, the...
A 3-phase 138-kv transmission line is connected to a 49 MW load at .85 lagging power factor. The line constants of the 52-mile long line are Z = 95 L 78 degree ohm and Y=.001 L90 degree S. Using the nominal T Circuit representation, calculate the A, B, C, and D constants of the line Sending-end voltage Sending-end current Sending-end power factor Efficiency of transmission
A transmission line with characteristic impedance of 100 ? is connected to a 200+j400 ? load. Use Smith chart to calculate (i) standing wave ratio (ii) reflection coefficient (iii) lengths and locations of a short circuited shunt stub to match the load to the transmission line.
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
The six-bus system shown in Figure 1 will be simulated using MATLAB. Transmission line data and bus data are given in Tables 1 and 2 respectively. The transmission line data are calculated on 100 MVA base and 230 (line-to-line) kV base for generator. Tasks: 1. Determine the network admittance matrix Y 2. Find the load flow solution using Gauss-Seidel/Newton Raphson method until first iteration by manual calculation. Use Maltab software to solve power flow problem using Gauss-Seidel method. Find the...
please follow instruction and solve every task in detail, thank you very much! A generator is connected to a transmission line system that is shown below. The system consists of two transmission lines, each with a characteristic impedance of 75 [2], connected to a load impedance of 75 [2]. These two lines are then fed by a single main feed line having a characteristic impedance 75 [2], which is fed by the generator (not shown). It is desired to have...
Qustion 2.120 marks) a) Figure I below shows a system with plant-I and plant-2 connected to bus-1 and bus-2 respectively. There are two loads and 3 branches. The bus-I is the reference bus with 1.040° pu voltage. Base MVA is 100 If the branch currents and branch impedance values are as follows -2.5-j0.50pu -2-j040 pu I 1.5-j0.3 pu Calculate: 7-0.05+j0.20 pu -0.02+j0.08 pu Z 0.025+j0.10 pu i. Current distribution factors (4 marks) ii. Power factor angles at bus 1 and...
Question L(20 marks) The variable operating costs of three generators a power system connected in are as follows: The generator limits are: 100 s P S 400 MW 150 S P2 s 500 MW The total transmission losses for the power system are given by: B=1.5×10-4 P/ + 2 x 10-sPgPg + 3 × 10-sp/ Mw Given λ 16.00 SMfw hr Determine: i. Output of each unit (6 marks) ii. Total transmission losses (3 marks) ii. Total load demand (2...