Question

30,000 kW at power factor 0·8 lagging is being transmitted over a 220 kV, three-phase transmission...

30,000 kW at power factor 0·8 lagging is being transmitted over a 220 kV, three-phase transmission line. The length of the line is 275 km and the efficiency of transmission is 90%. Calculate the weight of copper required. Also calculate the weight of copper had the power been transmitted over a single-phase transmission line for the same line voltage and losses. Assume that the resistance of 1 km long conductor and 1 sq. cm is 0·l73 Ω and specific gravity of copper is 8·9.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solution:

(i) Total power transmitted = 30000 kW

Power factor = 0.8

We know that for a three phase system total power,

P = 3.ViIcos

therefore line current is,

30000 x 10 P 98.415.A V3.VICOS 3 x 220 x 103 x 0.8

Transmission Efficiency is 90%, therefore total losses W in line is 10% of transmitted power.

W= 30000\times \frac{10}{100}=3000kW

We know that total copper losses in the line,

W= 3.I_{L}^{2}R=3.I_{L}^{2}\left ( \frac{\rho l}{a} \right )

where l is length and a is cross-sectional area.

therefore,

pl 3000 x 103kW 3.1Z а

a=\frac{3.I_{L}^{2}.\rho l}{3000\times 10^{3}}

therefore cross-sectional area,

a=\frac{3\times 98.415^{2}\times 0.173\times 275}{3000\times 10^{3}}=0.46cm^{2}=0.46\times 10^{-4}m^{2}

Now volume of copper required,

3al 3 x (0.46 x 104) x (275 x 103) = 38.015m3 Volume

Specific gravity of copper=8.9

density of copper=8.9X1000=8900 kg/cubic meters

Weight of copper required,

{\color{Red} Weight=Volume\times density=38.015\times 8900=338333 Kg}

(ii) for single phase 2 wire system,

Total power,

P=V_{L}I_{L}cos\phi

therefore line current is,

I_{L} =\frac{P}{V_{L}cos\phi}=\frac{30000\times 10^{3}}{220\times 10^{3}\times 0.8}=170.45A

Transmission Efficiency is 90%, therefore total losses W in line is 10% of transmitted power.

W= 30000\times \frac{10}{100}=3000kW

We know that for two wire,total copper losses in the line,

W= 2.I_{L}^{2}R=2.I_{L}^{2}\left ( \frac{\rho l}{a} \right )

where l is length and a is cross-sectional area.

therefore,

2.I_{L}^{2}\left ( \frac{\rho l}{a} \right )=3000\times 10^{3}kW

a=\frac{2.I_{L}^{2}.\rho l}{3000\times 10^{3}}

therefore cross-sectional area,

a=\frac{2\times 170.45^{2}\times 0.173\times 275}{3000\times 10^{3}}=0.921cm^{2}=0.921\times 10^{-4}m^{2}

Now volume of copper required,

Volume=2al=2\times (0.921\times 10^{-4})\times (275\times10^{3})=50.655 m^{3}

Specific gravity of copper=8.9

density of copper=8.9X1000=8900 kg/cubic meters

Weight of copper required,

{\color{Red} Weight=Volume\times density=50.655\times 8900=450829 Kg}

Add a comment
Know the answer?
Add Answer to:
30,000 kW at power factor 0·8 lagging is being transmitted over a 220 kV, three-phase transmission...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A....

    3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A. The values of resistance, inductance and capacitance per phase per kilometre are 0.078 12, 1.056 mH and 0.029 F, respectively. The receiving-end voltage is 275 kV when full load is transmitted at 0.9 power factor lagging. Calculate the sending-end voltage and current, and the transmission efficiency, and com- pare with the answer obtained by the short-line representation. Use the nomi- nal n and T...

  • A three-phase overhead transmission line is designed to deliver 100 MVA at 220 kV line voltage...

    A three-phase overhead transmission line is designed to deliver 100 MVA at 220 kV line voltage over a distance of 100 km. If the I2R losses need to be kept to max of 3% of the rated line MVA, given the resistivity of the conductor material to be 2.84 x 10-8 W-m, determine the required conductor diameter and the conductor size in circular mils

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1 * 10^-6 s/km. Calculate the ABCD constants of this transmission line. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11. What is the efficiency of the...

  • A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2...

    A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 ohm/km, x = 0.88 ohm/km, y = 4.1 * 10^-6 S/km. 10. Calculate the ABCD constants of this transmission line. 11. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? 12. What is the voltage regulation of the transmission line for the conditions in question 11. 13. What is...

  • Two three-phase power transmission lines with a nominal operating voltage of 220 kV and a frequency...

    Two three-phase power transmission lines with a nominal operating voltage of 220 kV and a frequency of 60 Hz are connected in series as shown below. Per-phase constants of the first 110 km long energy transmission line (E.İ.H.-1); r = 0.01035Ω / km, L = 1.554 mH / km, and C = 7.387 ∙ 10-3 µF / km. Constants per phase of the second 100 km long energy transmission line (E.İ.H.2); Zh = 1.035 + j58.58 Ω / phase and...

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor...

    A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor of 0.85 lagging and 33-kV. If the series impedance of the line is 20+j30 Ohms/phase, calculate The ABCD constants (parameters) The sending end voltage The load angle The voltage regulation The transmission efficiency

  • 3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase...

    3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase wve-connected load connected to its receiving-end terminals, the voltage at the receiving end is 345kV. a) Find the complex load impedance per phase. b) Find the real and reactive power per phase. 15 pts.

  • UTORIAL PROBLEMS 1 A 150 km 34, 110 kV, 50 Hz transmission line transmits a load...

    UTORIAL PROBLEMS 1 A 150 km 34, 110 kV, 50 Hz transmission line transmits a load of 40,000 kw at 0-8 pf lagging at the receiving end. Resistance/km/phase-0-15Ω ; reactance/km/phase :06 Ω; susceptance km phase 10 S. Determine (i) the A, B, C and D constants of the line (ii) regulation of the line. [(i) A = D = 0.968 <1° ; B = 92-8 <7.5°Ω ; C 0.00145く90-5° S (ii) 33-5%)!

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT