Question

Moist air enters a cooling coil at 27°C DBT and 60 percent relative humidity at a...

Moist air enters a cooling coil at 27°C DBT and 60 percent relative humidity at a flow rate of 1.15 kg/s and leaves at 16°C DBT and 90 percent relative humidity. Calculate the latente load on the coil, the sensible heat ratio and the bypass factor.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

. coel Inlet condition of moist air at cooling T, = 27°C dry bulb temperature 8, = 60% = Relative humidity Outlet condition Tria Chi-ha) ås from psychrometric chart, T₂ = 16°c (DBT & Ra=90% RH at h₂ = 42 kJ/kg Qs = 1.15 (53 - 42) ås = 12.65 12.65 kWTade = 13°c 16-13 BP = = 0.214 27 - 13 BPF 0.214 (4-14) ow= I specific Humidi (110 Lap 88/8) 1 Qs malni - ha) T2 Ti Tadp Dry100 105 110 115 120 kJ/kg/d.a) 30 29 29 ..0- - 0.8 -10.0 28 10.00 20 -5.0 8.0 -0.7 7.0 6.0 +0.6 SENSIBLE HEAT TOTAL HEAT -4.0100 105 110 115 120 kJ/kg/d.a) 30 95 29 -1.0- .- 00 8:9 10.007 -0.8 -10.0 1.5 +5.0 2.0 27 1.6 6.0 - 1.0 SENSIBLE HEAT TOTAL H

Add a comment
Know the answer?
Add Answer to:
Moist air enters a cooling coil at 27°C DBT and 60 percent relative humidity at a...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT