Question

Water entering a wet cooling tower at 35°C at a rate of 100 kg/s is cooled to 22°C in the cooling tower by air that enters the tower at 1 atm, 20°C, and 60% relative humidity and leaves saturated at 30°C. The makeup water of 22°C is supplied to the outlet to make the mass flow rate of the cool water the same as that at the inlet, see Figure Q5.

Q.5Water entering a wet cooling tower at 35°C at a rate of 100 kg/s is cooled to 22°C in the cooling tower by air that enters

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Substituting values in ma expression ma 100 C146 64-3228) 96.9 Ks/sec (lo0-42 2) CO 0213-0 0087) 32-28 . Volume flono rate of

Add a comment
Know the answer?
Add Answer to:
Water entering a wet cooling tower at 35°C at a rate of 100 kg/s is cooled to 22°C in the cooling tower by air that enters the tower at 1 atm, 20°C, and 60% relative humidity and leaves saturated at 3...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 4. Liquid water at 100°F and 200 gal/min volumetric flow rate enters a cooling tower operating...

    4. Liquid water at 100°F and 200 gal/min volumetric flow rate enters a cooling tower operating at steady state. Atmospheric air enters with a dry-bulb temperature of 80°F and a wet-bulb temperature of 60°F. Moist air exits the cooling tower at 90° and 90% relative humidity. Makeup water is provided at 80°F. Calculate the mass flow rates of the dry air and makeup water, each in lb/min, versus return water temperature at 80, 90, and 100°F. Ignore kinetic and potential...

  • If the cooling water (cp = 4180 J/kg·ºC) from the above problem is to be provided...

    If the cooling water (cp = 4180 J/kg·ºC) from the above problem is to be provided evenly by 10 cooling towers. Humid air enters each tower at 1 atm, 15 ºC and 20% relative humidity, and leaves at 20 ºC and 0.014 kg of water/kg of dry air. Determine the required volume flow rate of air through each cooling tower. Air exit 20 °C, 0 = 0.014 kg of water/kg of air Warm water 40 °C Air inlet 1 atm...

  • Air is at 1 atm, 40°C, and 20 percent relative humidity. Water at 22°C is evaporated...

    Air is at 1 atm, 40°C, and 20 percent relative humidity. Water at 22°C is evaporated into this air to produce air at 25°C and 80 percent relative humidity. How much water, in kg H2O/kg dry air, is required and how much cooling, in kJ/kg dry air, has been produced? Use data from the tables. Please help solve the amount of cooling produced. I believe I am reading the psychrometric chart incorrectly Water T c Humidifier 1 atm 40? 20%...

  • Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating...

    Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. Using data from the psychrometric chart, determine: (a) the humidity ratio of the entering moist air mixture, in kg(vapor) per kg(dry air). (b)...

  • In a cooling tower, air at 20°C and 50% RH enters the tower at a rate...

    In a cooling tower, air at 20°C and 50% RH enters the tower at a rate of 20 m3 /s and leaves at 28°C and 85% RH. The water leaving the tower is 10°C cooler than the water entering the tower. Assume specific heat of water is 4.19 kJ/kg K. Determine i. The mass flow rate of water in kg/s ii. Mass flow rate of make-up water in kg/s

  • corn containing 5% water. Dry air enters the dryer at 70°C and 1 atm and the...

    corn containing 5% water. Dry air enters the dryer at 70°C and 1 atm and the outlet air is at 55°C with a relative humidity of 50%. Calculate the mass flowrate of corn enters the dryer and volumetric flow rate of inlet air. containing 55% water enters a continuous tunnel dryer and leaves at a rate of 500 kg/h

  • Mass Flow Rate Problem

    Water exiting the condenser of a power plant at 38ºC enters a cooling tower with a massflow rate of 4.5 x 107 kg/h. A stream of cooled water is returned to the condenser from acooling tower with a temperature of 30ºC and the same flow rate. Makeup water is addedin a separate stream at 20ºC. Atmospheric air enters the cooling tower at 25ºC and 35%relative humidity. Moist air exits the tower at 30ºC and 95% relative humidity.Determine the mass flow...

  • a) Define relative humidity (2 marks) b) Describe the relation between relative humidity, the capacity of...

    a) Define relative humidity (2 marks) b) Describe the relation between relative humidity, the capacity of air to hold moisture a ambient temperature. (2 marks) c) Moist air at 22°C and a wet bulb temperature of 9°C enters a steam spray humidifier. The mass flow of the dry air is 90 kg/min. Saturated water vapor at 110 °C is injected into the mixture at a rate of 52 kg/hr. There is no heat transfer with the surroundings, and the pressure...

  • The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling...

    The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...

  • H1- COOLING TOWER [10 p] 1. What is the wet bulb temperature? How can you measure...

    H1- COOLING TOWER [10 p] 1. What is the wet bulb temperature? How can you measure it? Is the wet-bulb temperature greater than dry-bulb temperature? Why? [10 p] 2. A cooling tower is to be designed to cool 8 kg/s of water from 37°C to 29 °C. Entering air is 25 °C and at 30 % relative humidity. Leaving air is 22 °C and at 90% relative humidity. a) Calculate the air flow rate, G. b) Determine the possible lowest...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT