Water entering a wet cooling tower at 35°C at a rate of 100 kg/s is cooled to 22°C in the cooling tower by air that enters the tower at 1 atm, 20°C, and 60% relative humidity and leaves saturated at 30°C. The makeup water of 22°C is supplied to the outlet to make the mass flow rate of the cool water the same as that at the inlet, see Figure Q5.
Water entering a wet cooling tower at 35°C at a rate of 100 kg/s is cooled to 22°C in the cooling tower by air that enters the tower at 1 atm, 20°C, and 60% relative humidity and leaves saturated at 3...
4. Liquid water at 100°F and 200 gal/min volumetric flow rate enters a cooling tower operating at steady state. Atmospheric air enters with a dry-bulb temperature of 80°F and a wet-bulb temperature of 60°F. Moist air exits the cooling tower at 90° and 90% relative humidity. Makeup water is provided at 80°F. Calculate the mass flow rates of the dry air and makeup water, each in lb/min, versus return water temperature at 80, 90, and 100°F. Ignore kinetic and potential...
If the cooling water (cp = 4180 J/kg·ºC) from the above problem is to be provided evenly by 10 cooling towers. Humid air enters each tower at 1 atm, 15 ºC and 20% relative humidity, and leaves at 20 ºC and 0.014 kg of water/kg of dry air. Determine the required volume flow rate of air through each cooling tower. Air exit 20 °C, 0 = 0.014 kg of water/kg of air Warm water 40 °C Air inlet 1 atm...
Air is at 1 atm, 40°C, and 20 percent relative humidity. Water at 22°C is evaporated into this air to produce air at 25°C and 80 percent relative humidity. How much water, in kg H2O/kg dry air, is required and how much cooling, in kJ/kg dry air, has been produced? Use data from the tables. Please help solve the amount of cooling produced. I believe I am reading the psychrometric chart incorrectly Water T c Humidifier 1 atm 40? 20%...
Moist air at 24°C, 1 atm, and 35% relative humidity enters an evaporative cooling unit operating at steady state consisting of a heating section followed by a soaked pad evaporative cooler operating adiabatically. The air passing through the heating section is heated to 45°C. Next, the air passes through a soaked pad exiting with 50% relative humidity. Using data from the psychrometric chart, determine: (a) the humidity ratio of the entering moist air mixture, in kg(vapor) per kg(dry air). (b)...
In a cooling tower, air at 20°C and 50% RH enters the tower at a rate of 20 m3 /s and leaves at 28°C and 85% RH. The water leaving the tower is 10°C cooler than the water entering the tower. Assume specific heat of water is 4.19 kJ/kg K. Determine i. The mass flow rate of water in kg/s ii. Mass flow rate of make-up water in kg/s
corn containing 5% water. Dry air enters the dryer at 70°C and 1 atm and the outlet air is at 55°C with a relative humidity of 50%. Calculate the mass flowrate of corn enters the dryer and volumetric flow rate of inlet air. containing 55% water enters a continuous tunnel dryer and leaves at a rate of 500 kg/h
Water exiting the condenser of a power plant at 38ºC enters a cooling tower with a massflow rate of 4.5 x 107 kg/h. A stream of cooled water is returned to the condenser from acooling tower with a temperature of 30ºC and the same flow rate. Makeup water is addedin a separate stream at 20ºC. Atmospheric air enters the cooling tower at 25ºC and 35%relative humidity. Moist air exits the tower at 30ºC and 95% relative humidity.Determine the mass flow...
a) Define relative humidity (2 marks) b) Describe the relation between relative humidity, the capacity of air to hold moisture a ambient temperature. (2 marks) c) Moist air at 22°C and a wet bulb temperature of 9°C enters a steam spray humidifier. The mass flow of the dry air is 90 kg/min. Saturated water vapor at 110 °C is injected into the mixture at a rate of 52 kg/hr. There is no heat transfer with the surroundings, and the pressure...
The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...
H1- COOLING TOWER [10 p] 1. What is the wet bulb temperature? How can you measure it? Is the wet-bulb temperature greater than dry-bulb temperature? Why? [10 p] 2. A cooling tower is to be designed to cool 8 kg/s of water from 37°C to 29 °C. Entering air is 25 °C and at 30 % relative humidity. Leaving air is 22 °C and at 90% relative humidity. a) Calculate the air flow rate, G. b) Determine the possible lowest...