Question

4. A 1.5-m rigid tank is initially empty. Refrigerant (R-134a) in the supply line at 750kPa and 20°C is connected to the well
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Assumptions - This is an unsteady process, Since the condinons within the devices are changing during the process, but it can

Add a comment
Know the answer?
Add Answer to:
4. A 1.5-m rigid tank is initially empty. Refrigerant (R-134a) in the supply line at 750kPa...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 0.145 m rigid tank initially contains refrigerant-134a at 1 MPa and 100 percent quality. The...

    A 0.145 m rigid tank initially contains refrigerant-134a at 1 MPa and 100 percent quality. The tank is connected by a valve to a supply line that carries refrigerant-134a ad.2 MPa and 36°C. Now the valre is opened, and the refrigerant is allowed to enter the tank. The valve is closed when it is observed that the tank contains saturated liquid atl.2 MPa. Determine (a) the mass of the refrigerant that has entered the tank 156.057g(Kound to three decimal places)...

  • An insulated, rigid tank that is initially evacuated is connected by a valve to a nitrogen...

    An insulated, rigid tank that is initially evacuated is connected by a valve to a nitrogen supply line. The nitrogen in the line flows at 30°C and 80 kPa. The valve is then opened and nitrogen flows into the tank until the pressure reaches 80 kPa; at which point the valve is closed. Using constant specific heats at room temperature (Cp = 1.039 kJ/kgK, Cv = 0.743 kJ/kgK, k. = 1.3984), determine the final temperature of the nitrogen in the...

  • 0.4 kg of Refrigerant 134a initially fills a piston–cylinder device with a volume of 15 L...

    0.4 kg of Refrigerant 134a initially fills a piston–cylinder device with a volume of 15 L at a pressure of 400 kPa. The cylinder is connected to a supply line through a valve. R-134a is flowing in the supply line at 900 kPa and 45°C. The valve is opened, and R-134a is allowed to enter the cylinder. The valve is closed when the volume of the cylinder is triple and the temperature in the cylinder reaches 15°C. During the process,...

  • A 0.7-m3 rigid tank contains refrigerant-134a initially at 160 kPa and 40 percent quality. Heat is...

    A 0.7-m3 rigid tank contains refrigerant-134a initially at 160 kPa and 40 percent quality. Heat is now transferred to the refrigerant until the pressure reaches 600 kPa. Determine the amount of heat transferred.

  • 1- A fixed mass rigid tank is filled with Refrigerant-134a. Assuming initially, R-134a is under 160...

    1- A fixed mass rigid tank is filled with Refrigerant-134a. Assuming initially, R-134a is under 160 psia and saturated condition (quality, x, = 1.0). The volume of tank is 20 ft. Then it went through a process until the final pressure, P, reduced to 50 psia, and the heat transfer occurred during this process. Determine (a) the final temperature, (b) the amount of R-134a been condensed, (c) the net heat transfer. (15 points)

  • NEED HELP A rigid, poorly insulated tank with a volume of V1.0 m3 initially contains a...

    NEED HELP A rigid, poorly insulated tank with a volume of V1.0 m3 initially contains a saturated water vapor (quality of 1.0) at a pressure of 3 bars (300 kPa). The tank is connected to a supply line valve is opened and 2.0 kg of steam enters the rigid tank, after which the valve is closed. The pressure is measured after the valve is closed and it is found that p2-5 bars (500 kPa). Find (a) the state of the...

  • SP04 A rigid, poorly insulated tank with a volume of V1.0 m3 initially contains a saturated...

    SP04 A rigid, poorly insulated tank with a volume of V1.0 m3 initially contains a saturated water vapor (quality of 1.0) at a pressure of 3 bars (300 kPa). The tank is connected to a supply line containing steam at a pressure of pL- 10 bars (1000 kPa) and a temperature of TL 500°C. The valve is opened and 2.0 kg of steam enters the rigid tank, after which the valve is closed. The pressure is measured after the valve...

  • A closed, rigid tank contains R-134a, initially at 100°C. The refrigerant is cooled until it has...

    A closed, rigid tank contains R-134a, initially at 100°C. The refrigerant is cooled until it has a quality of 98.26% at 20°C. For the refrigerant, determine: a. (3) A T-v diagram labeling state 1 and 2 b. (12) The initial and final pressures, in bar c. (10) The heat transfer and work for the process, each in kJ/kg

  • A 2.2-m3 rigid tank initially contains air at 100 kPa and 22°C. The tank is connected...

    A 2.2-m3 rigid tank initially contains air at 100 kPa and 22°C. The tank is connected to a supply line through a valve. Air is flowing in the supply line at 600 kPa and 22°C. The valve is opened, and air is allowed to enter the tank until the pressure in the tank reaches the line pressure, at which point the valve is closed. A thermometer placed in the tank indicates that the air temperature at the final state is...

  • A 0.6 m3 rigid tank initially contains refrigerant-134a in saturated vapor form at 0.9 MPa ....

    A 0.6 m3 rigid tank initially contains refrigerant-134a in saturated vapor form at 0.9 MPa . As a result of heat transfer from the refrigerant, the pressure drops to 240 kPa. Use TESTCalc to answer the following questions. a) Determine the final temperature (T2). b) Determine the amount of refrigerant that condenses. c) Determine the heat transfer (Q).

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT