If you have any doubts pls mention in the comments I'll clarify it...
Pls upvote if u like the answer..
a) What is the three phase system? b) What is the role of Neutral wire in...
THREE-PHASE, FOUR-WIRE SYSTEMS, NEUTRAL CURRENT 5-21 In the three-phase, four-wire system of Fig. 5-28, all single-phase rectifier loads are identical and the conditions are such that each line current flows for less than 60 during each half-cycle of the line-to-neutral voltage. Show that in terms of their rms values,-V311
In the balanced three-phase, four-wire system of Fig. 5-28 with v 180 sin(400t), all single-phase rectifier systems are identical and each current source is 10A. (a) Find DF value of the input i (b) Find the rms value of i, and the neutral current i, (c) Find the power factor. 추 phase rectifier system ib Fig. 5-28 In the balanced three-phase, four-wire system of Fig. 5-28 with v 180 sin(400t), all single-phase rectifier systems are identical and each current source...
20. In a two-phase three-wire system if the phase currents are 1-4.3+j7.9 A and I, 2.4 + j6.5 A, what is the value of the current in the common wire? A. 1.9 +j14.4 A B. 2.2 + j5.5 A C. 4.1 +j12.2 A D. 6.7 +j1.4 A 4
an open delta three phase transformer system has one transformer center tap that provide in neutral for single phase voltage. if the voltage from line to center tap 277 volt ,what is high leg voltage?
9. Assuming we found the neutral to line capacitance per phase of a three phase line as 8.61x 10 12 F/m, what is the shunt admittance to neutral in S/m or mhos / m? a. 8.61 x 10-9 S/m b. 7.73 x 10-9 S/m c. 3.25 x 10-9 S/m d. 2.22 x 10-9 S/m 10. For a single phase line with two 3/0 12 strand copper conductors spaced 6 ft between centers. Determine the line to line capacitance Cxy in...
Please show all the steps A 60-Hz three-phase, three-wire overhead line has solid cylindrical conductors arranged in the form of an equilateral triangle with 4 ft conductor spacing. Conductor diameter is 0.5 in a) Calculate the positive-sequence inductance in H/m and the positive-sequence inductive reactance in 2/km. b) Calculate the capacitance-to-neutral in F/m and the admittance-to-neutral in S/km for the three-phase line stated above. Neglect the effect of the earth plane. c) Rework b) if the phase spacing is i)...
Homework 24: Use the ALCOA conductor table from Glover, Sarma, Power System Analysis and Design, for this assignment A 12 kV 60 Hz three-phase three-wire overhead line has Drake ACSR conductors spaced 4 ft apart in an equilateral triangle. It is operating at 50 degrees C. a. Calculate resistance (0.1288 ohms/mile) of one phase of the line b. Calculate series inductance of the line (0.93 uH/m) c. Calculate shunt capacitance of the line. (12.47 pF/m) The line is 20 km...
Problem5 A balanced Y-Y four-wire system has phase voltages Van-1 10L0。V, Vbn-1104200 V, Ven 1102-1200 V. The load impedance per phase is 19 +j13 2, and the line impedance per phase is 1+,2 Ω. a) Construct the a-phase equivalent circuit of the system. b) Calculate the line currents and neutral current. c) Calculate the three phase voltages at the load VAN, VBN and Vcv d) Calculate the average power per phase delivered to the Y- connected load
What is the effect of neutral connections in three-phase wye connected circuits?
A three-wire 120/240-V system supplies a load of 2.4 kW at 120 V on phase A, 4.8 kW on phase B and 6.4 kW at 240 V. The power factor for each load is 1.0. Draw a diagram of the residential system. Find the currents in each of the three legs.