Question

Question 1

In the circuit shown, find V. 41-90° V 40 212 212 24/0° v (5) +-j412 322 v. Ideal

Question 2

A 13.8-KV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 per phas

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Oiven circuit - 42-90 452 su tona R2 j X2 anom + o I 131 O tako Ltd, je Divechim of In indicated based on Dot Convention. 242- 24 -42-90° 25+ 2.5 +10 5+1007 7-10 11 : 0.440367+1-4678 Va (0.617 + jo-14] - V8 (0.367-jo!!] = 5:56-j1:46789 - 0 Nodal equaBy Direct Analysis Vo = Vó = 1.317-20.48 and Vo=-2V6 i. Vo =(1.317-30.48)x-2: -2.634 +20.96 Los Vo = 2.80_160° volts Hence O

As per Chegg's answering guidelines we are supposed to answer only one question at once. Hence i have answered the first question completely with explanation and steps. Please repost the other questions separately to get their solution.

Add a comment
Know the answer?
Add Answer to:
Question 1 Question 2 In the circuit shown, find V. 41-90° V 40 212 212 24/0°...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of thi...

    HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...

  • HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator...

    HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...

  • A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a...

    A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. This generator is operating in parallel with a large power system (infinite bus). At the absolute maximum power possible, how much reactive power will this generator be supplying or consuming? Sketch the corresponding phasor diagram. (Assume IF is still unchanged.)

  • A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7...

    A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7 Q and a negligible armature resistance. I) What is the magnitude of the internal generated voltage at rated conditions? 2) What is its torque angle at these conditions? 3) What is its voltage regulation? 4) Ignoring the losses in this generator, what torque must be applied to its shaft by the prime mover at full load? 5) What is the maximum power the generator...

  • (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utili...

    please show steps. Thank you. (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utility) bus to deliver power to a 2000 kw plant load at 0.866 lagging power factor. The synchronous generator is wye-connected and rated 3750 kva, 13.2 kv, and 0.8 power factor lagging with 1.0 per unit synchronous reactance and negligible armature resistance. 13.2 kVI 60 Hz I infinite bus utility) rated: 3750 kva 0.8 lag load: 2000 kW...

  • Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generat...

    Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...

  • A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full...

    A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full load armature current is 60 A at 0.8 pf lagging. Under full load conditions, the friction and windage losses are 1.5 kW, and core losses are 1 kW at 50 Hz. Ignore armature copper losses. The field has been adjusted so that the terminal voltage is 480 V at no load. a.What is the speed of rotation of this gen? b.What is the generator...

  • A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system....

    A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system. The generator is delivering its rated output power, under which conditions pfload = 0.8 lagging and |SI = 20 MVA. The generator per-phase model parameters at rated load are. RA = 0.5 2 Xss = 522 9. What is the generator's line-to-line voltage regulation? Is the voltage regulation positive or negative? 10. If the field current is held at the rated load value, but...

  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and...

    Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and armature resistance, Ra-005Ω. The terminal voltage in all working conditions is assumed constant and equal to the rated voltage. The generator is delivering a load current of 2000A at 0.8 PF leading a. Draw the per-phase equivalent circuit of the generator. b. Calculate the induced EMF, EA. c. Calculate the real and reactive power delivered at the generator terminals. d. Sketch the phasor diagram...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT