A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a...

A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. This generator is operating in parallel with a large power system (infinite bus). At the absolute maximum power possible, how much reactive power will this generator be supplying or consuming? Sketch the corresponding phasor diagram. (Assume IF is still unchanged.)

0 0
Add a comment Improve this question Transcribed image text
Answer #1

We know the Power flow Equation of Alternator P= EV COSC0-8) v² Zs Cosa Zs Zs Zs Q = Ev sin(0-8) sing Where, E = Internal volZs = 1:5+j12 Zs 12.09282.89 Q = -V² sino Zs Q = -(13-) sin( 82. 89 P= (12-09) - 15.62MWAR Phagor dagl.com ml s=82-8° Q = 36.8

Add a comment
Know the answer?
Add Answer to:
A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60...

    A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60 Hz, assume that the generator is connected to a 3200-V infinite bus, and that its field current has been adjusted so that it is supplying rated power at 0.9 factor lag to the bus. Xs=1.5 Ohm, You may ignore the armature resistance RA when answering the following questions. What will happen to the real and reactive power supplied by this generator if the field...

  • A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has...

    A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has X-20 Ω per phase and Ra 2 Ω per phase. The generator is connected to an infinite bus (a) (i) Determine the excitation voltage at the rated condition (ii) Draw the phasor diagram for the condition (b) Determine the torque angle at the rated condition (c) If the field current is kept constant, determine the maximum power the generator can supply (d) (i) For...

  • 3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and...

    3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.

  • Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generat...

    Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...

  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a...

    A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of XS=0.016 Ω and an armature resistance of RA=0.016 Ω. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the...

  • HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of thi...

    HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...

  • A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7...

    A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7 Q and a negligible armature resistance. I) What is the magnitude of the internal generated voltage at rated conditions? 2) What is its torque angle at these conditions? 3) What is its voltage regulation? 4) Ignoring the losses in this generator, what torque must be applied to its shaft by the prime mover at full load? 5) What is the maximum power the generator...

  • A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X=...

    A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X= 9 Ω per phase and a negligible resistance. The generator is delivrimg rated power at a 0.8 power factor lagging at the rated terminal voltage to an infinitie bus, as shown in the following figure 1. Figure 1.The synchronous generator connected to infinite bus in single phase. 1)   The excitation voltage is E = 26.87 KV, The generator delivring 60 MW. Compute the powe...

  • A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a...

    A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT