Question

A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X= 9 per phase and a negligible resistance. The generator is delivrimg rated power at a 0.8 power factor lagging at the rated terminal voltage to an infinitie bus, as shown in the following figure 1.

E/8 X 8 Ιφ V.0

Figure 1.The synchronous generator connected to infinite bus in single phase.

1)   The excitation voltage is E = 26.87 KV, The generator delivring 60 MW. Compute the powe angle δ , the armature current I ,the power factor PF  ? when the field current is adjusted for the following excitation:

*The excitation voltage is decreased to 89.8 percent (89.8%) of the value E ?

A.

δ = 25.6°   I= 1832A   = -26. 52°   cos =   0.895 Lag

B.

None of these

C.

δ = 27.6°   I= 1732A   = -26. 52°   cos =   0.895 Lead

D.

δ = 27.6°   I= 1732A   = -26. 52°   cos =   0.895 Lag

0 0
Add a comment Improve this question Transcribed image text
Answer #1

ELS Х Given 2000 ILO 25 x=92 given TS MVA , 85kV & t/ph © The excitation voltage E = 26.87 KV. Three phase active power = 60P= constant EV sins X Esins = constant Esins, & sind sinsz = sins, Ez EI sin Ei 10.89851 sim (270) = 31-05° Ia Es-vé X 90 sin

Add a comment
Know the answer?
Add Answer to:
A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X=...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of...

    A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of 12 2 and negligible stator resistance. a. The generator is connected to an infinite bus and delivers 80 MW at 0.8 leading power factor. Determine the power angle and excitation voltage EA. Draw the phasor diagram. b. The field current of the generator is now slowly reduced until the generator reaches its static stability limit (5=0). For this condition, determine the power angle, excitation...

  • 3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and...

    3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.

  • A three-phase synchronous generator with rated data VM = 20 kV, SM = 100 MVA, n...

    A three-phase synchronous generator with rated data VM = 20 kV, SM = 100 MVA, n = 500 rpm is driven by a turbine that can provide a maximum of 1.6 MNm. Synchronous reactance, XS = 3Ω / phase. The armature resistance (Ra ) is neglected. In open circuit mode (P = 0), an excitation current of 300 A is required to obtain rated voltage (VM ). The machine should be phased into a strong grid, 3x20 kV, 50 Hz....

  • Please show all the clearly step A 500 MVA, 24 kV, 60 Hz three-phase synchronous generator...

    Please show all the clearly step A 500 MVA, 24 kV, 60 Hz three-phase synchronous generator is operating at rated voltage and frequency with a terminal power factor of 0.8 lagging. The synchronous reactance X 0.8. Stator coil resistance is negligible. The internally generated voltage E,-18 kv a) Draw the per phase equivalent circuit. b) Determine the torque (power) angle 5, c) the total output power, d) the line current.

  • Problem #2: A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses...

    Problem #2: A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (5), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained...

  • QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase...

    QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase reactance Xg of 1.5 pu and supplies 0.8 pu per phase real power (P) at the rated voltage, with a lagging power factor of 0.6 to the load. Find the actual excitation voltage Vo in kV (line value). 96.392

  • A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has...

    A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has X-20 Ω per phase and Ra 2 Ω per phase. The generator is connected to an infinite bus (a) (i) Determine the excitation voltage at the rated condition (ii) Draw the phasor diagram for the condition (b) Determine the torque angle at the rated condition (c) If the field current is kept constant, determine the maximum power the generator can supply (d) (i) For...

  • (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utili...

    please show steps. Thank you. (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utility) bus to deliver power to a 2000 kw plant load at 0.866 lagging power factor. The synchronous generator is wye-connected and rated 3750 kva, 13.2 kv, and 0.8 power factor lagging with 1.0 per unit synchronous reactance and negligible armature resistance. 13.2 kVI 60 Hz I infinite bus utility) rated: 3750 kva 0.8 lag load: 2000 kW...

  • A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60...

    A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60 Hz, assume that the generator is connected to a 3200-V infinite bus, and that its field current has been adjusted so that it is supplying rated power at 0.9 factor lag to the bus. Xs=1.5 Ohm, You may ignore the armature resistance RA when answering the following questions. What will happen to the real and reactive power supplied by this generator if the field...